Search for tools and product advice,

Discuss Novel gas main bonding in the UK Electrical Forum area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
Thought I was onto a real winner today when checking the gas bond to find a nice bonding conductor run directly to a local earth rod:

2020-09-28 15.06.50.jpg


The main house is currently TT with a rod on the opposite side of the house, so maybe they thought the foundations counted as a massive MET :rolleyes:

Was all set to run cabling round the house, but as it happens, further testing between the MET and this showed very low resistance (boiler cpc was my first guess), and when I delved into the CU there was a 10mm bonding conductor which goes maybe to the boiler in the attic, and gives a reading of 0.04 back to this pipe.

Means their current earth is effectively the gas pipe rather than either rod though, since Zs on my new lights outside is 2Ohmish, while Ze was 193...

DNO visit in a week or so hopefully will upgrade to PME.

Any reason electrically to remove this connector? Might stop the next guy thinking the same, though I will put a sticker inside the box or at the CU to clarify I think.
 
Yes, someone who totally missed the concept of equipotential bonding!

Given the good internal bond it is not really an issue, but as you say it ought to be documented or tidied up so no one gets confused in the future.
 
Yes, someone who totally missed the concept of equipotential bonding!

Given the good internal bond it is not really an issue, but as you say it ought to be documented or tidied up so no one gets confused in the future.
I did check rod to rod just to be sure, but many ohms difference of course...

Goes to show that testing bonding is sometimes beneficial though - Before I got my wander lead I would likely have just run a new one...
 

Reply to Novel gas main bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
715
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
992

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock