Discuss Off-peak consumer for storage heaters EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

understanding is this should be renewed and come March this year will become mandatory for all rental properties that all Electrical circuits are RCD protected.
We inspect against current regs.
So what in the current regs requires them to be RCD protected? They are not domestic lighting, not sockets, and not outside.
Often the only grounds for C2 would be impact protection for cables buried in walls <50mm which is normally difficult to determine on an EICR and no one has managed to drill into them yet!
Unless I have a good reason they are normally a C3 for me.

What new legislation is happening in March?
 
We inspect against current regs.
So what in the current regs requires them to be RCD protected? They are not domestic lighting, not sockets, and not outside.
Often the only grounds for C2 would be impact protection for cables buried in walls <50mm which is normally difficult to determine on an EICR and no one has managed to drill into them yet!
Unless I have a good reason they are normally a C3 for me.

What new legislation is happening in March?
From 01/03/2024 a key requirement is that all electrical installations must be protected by a residual current device (RCD). This is part of many other electrical requirements in rented properties in Scotland.
 
We inspect against current regs.
So what in the current regs requires them to be RCD protected? They are not domestic lighting, not sockets, and not outside.
Often the only grounds for C2 would be impact protection for cables buried in walls <50mm which is normally difficult to determine on an EICR and no one has managed to drill into them yet!
Unless I have a good reason they are normally a C3 for me.

What new legislation is happening in March?
All landlords have a legal obligation to ensure their property meets the Repairing Standard at the start of a tenancy and at all times during a tenancy. From 1 March next year (2024) the Repairing Standard is being changed to add the following requirements:-

  • water pipes must be free of lead (where this cannot be ascertained water testing must be carried out to check for the presence of lead piping)
  • electrical installations must be protected by a residual current device (RCD)
  • properties must have a fixed space heating system (a permanent installation in the property which is plumbed or hard wired and capable of maintaining a temperature of 21⁰C in at least one room and 18⁰C elsewhere, when the outside temperature is minus 1⁰C.)
  • installations for fuels other than gas and electricity to be in a reasonable state of repair and in proper working order
  • any common parts pertaining to the property must be able to be accessed and used safely
  • the property must have satisfactory provision for, and safe access to, a food storage area and food preparation space
  • where the property is in a tenement, common doors must be secure and fitted with satisfactory emergency exit locks and a secure entry system
 
From 01/03/2024 a key requirement is that all electrical installations must be protected by a residual current device (RCD). This is part of many other electrical requirements in rented properties in Scotland.

All landlords have a legal obligation to ensure their property meets the Repairing Standard at the start of a tenancy and at all times during a tenancy. From 1 March next year (2024) the Repairing Standard is being changed to add the following requirements:-

I'm still researching, but that appears to be the headline, and the detail seems to be:

D.55
In order to comply with the Repairing Standard, there must be one or more Residual Current Device (RCD) with rated residual operating current not exceeding 30 mA in the main or principal consumer unit. Normally, as a minimum, this will cover the socket-outlet circuit. However, the protection requirements will vary depending on the installation in the let property. As set out in D.60 – D.73, in order to comply with the Repairing Standard, landlords should ensure that an EICR is completed every five years. The EICR assesses the installation against BS 7671. This British Standard includes the requirements for RCD protection. Therefore, landlords should refer to the EICR report for the appropriate RCD protection for their installation. The absence of an RCD means that the house does not comply with the Repairing Standard.

Source: The Repairing Standard Statutory Guidance - https://www.gov.scot/publications/repairing-standard-statutory-guidance-private-landlords/pages/16/

To me, at face value, it is saying that socket circuits need protection, and an EICR against BS7671 applies for the remainder?
 
Last edited:
I'm still researching, but that appears to be the headline, and the detail seems to be:

D.55
In order to comply with the Repairing Standard, there must be one or more Residual Current Device (RCD) with rated residual operating current not exceeding 30 mA in the main or principal consumer unit. Normally, as a minimum, this will cover the socket-outlet circuit. However, the protection requirements will vary depending on the installation in the let property. As set out in D.60 – D.73, in order to comply with the Repairing Standard, landlords should ensure that an EICR is completed every five years. The EICR assesses the installation against BS 7671. This British Standard includes the requirements for RCD protection. Therefore, landlords should refer to the EICR report for the appropriate RCD protection for their installation. The absence of an RCD means that the house does not comply with the Repairing Standard.

Source: The Repairing Standard Statutory Guidance - https://www.gov.scot/publications/repairing-standard-statutory-guidance-private-landlords/pages/16/

To me, at face value, it is saying that socket circuits need protection, and an EICR against BS7671 applies for the remainder?
For me as the off peak consumer unit is a standalone board with no RCD, then we do not comply to the repairing standard as of March this year. As stated
The absence of an RCD means that the house does not comply with the Repairing Standard.
 
For me as the off peak consumer unit is a standalone board with no RCD, then we do not comply to the repairing standard as of March this year. As stated
For me, the off peak consumer unit is not the "main or principle consumer unit".

I have seen quite a few situations where over-zealous application of latest regulations against a budget has actually left things in a more dangerous condition dur to poor workmanship and materials.
I'm obviously not saying you would do that, but if everyone in Scotland changes every off-peak board then I bet the number of consumer unit fires will go up next year.
 

Reply to Off-peak consumer for storage heaters EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
if a house has economy 7, off peak board and on peak board. and where the meter only energizes the off peak board during the night for the storage...
Replies
2
Views
1K
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
599
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock