Not having much experience or knowledge of working with MK gear I thought I would ask a question of those more au fait with MK.

Have a job coming up where RCD protection is required for alterations over three circuits. The existing MCBs are MK LN59 BS3871 type 2. Does anyone know if a modern MK RCBO will fit with this older system to facilitate a cheaper option ?

If not then a board swap will be appropriate.

2016-09-08 11.08.20.jpg
 
Looking at your pic I think they do but I am not 100%, need someone else to confirm that.
 
Yeh they can fit but as they (the RCBO) are so long its a tight fit. Have done quite a few of those. The functional earth needs a crimped end to terminate it as its so fine.
 
i'd go for the board swap. them MCBs went out with the Titanic. who know what stresses they've suffered over years of abuse.
 
I don't like the sound of a tight fit with modern RCBOs. I think I will go back and add the cost of a board swap to the quote.

Thanks for the replies fellas.
 

Reply to Old MK Sentry in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
727
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Trying to locate a suitable RCBO for a Siemens board with (mostly) 5SX21 breakers in. They don't seem to make this range any more, though I...
Replies
2
Views
3K
Hello, We live in an old stone built ground floor flat, built in the 1880s. Obviously the consumer unit and cabling has been updated a number of...
Replies
94
Views
13K
Please take some time to read through this. It is written by Widdler's father. I found it on a governement website.. It certainly speaks my mind...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock