As L-S above, there isn't a supply labelled for the Off Peak Immersion and there would normally be a controller with time clock set to switch on the lower Off peak imersion on during the off peak hours for 2 or 3 hrs.
As noted above Off Peak is probably 7 hrs overnight and 3 during the day.
Re the water temperature and the thermostats, the lower due to it's location should be around 45c and upper (middle of cylinder) should only be around 50c max, to get 60c at the top.
If the water is still too hot when you have them set at 30c then the thermostats need replacing.
As noted above Off Peak is probably 7 hrs overnight and 3 during the day.
Re the water temperature and the thermostats, the lower due to it's location should be around 45c and upper (middle of cylinder) should only be around 50c max, to get 60c at the top.
If the water is still too hot when you have them set at 30c then the thermostats need replacing.