Discuss One touch light switches in the Lighting Forum area at ElectriciansForums.net

Reaction score
3
Looking for some advice on one touch switches to for a 2 way circuit.
Client is very particular and doesn't like it when switches forming 2 way or intermediate circuits enivitably end up in the wrong position. So I'm looking for switches that simply push on and then push off, similar to a retractive switch but remains on after activating....
 
Retractive switches are what you're after. Quinetic switches are retractive switches that require no wiring from the fitting to the switch position - the transceiver is attached at the ceiling rose/ light fitting) and the switch is self powering, requiring no batteries.

Quinetic switches are available from TLC, I've not seen any 3rd party equivalents from other wholesalers.
 
I thought a retractive switch had to be pressed and held on to keep the circuit live, and once you remove your finger the circuit is no longer live? Happy to be wrong on that as that makes the install very simple....
 
I thought a retractive switch had to be pressed and held on to keep the circuit live, and once you remove your finger the circuit is no longer live?
What you say is correct, but using the technology suggested, the momentary 'on' from the switch operates the control circuitry, which then turns on/off the light appropriately.
In the case of Quinetic remote switches, the mechanical push 'pings' a piezo electric generator, which creates power for a small rf transmitter that sends a signal to the receiver in the light circuit.
 
What you say is correct, but using the technology suggested, the momentary 'on' from the switch operates the control circuitry, which then turns on/off the light appropriately.
In the case of Quinetic remote switches, the mechanical push 'pings' a piezo electric generator, which creates power for a small rf transmitter that sends a signal to the receiver in the light circuit.
Just looked into the quinetic switching range, absolutely brilliant, that will work perfectly! They also do a scolmore click switch modual which will keep the same look from the rest of the house which is a bonus!
 
If you wanted a hardwired alternative, I have used 'Vadsbo' dimmer modules that can be located at any convenient position including a switch backbox and use any number of retractive switches to operate. The installation I did had 8 of them mounted in an adaptable box near the consumer unit and multiple switching pairs run out to the ridiculous number of switches the client requested. Result was happy customer, only criticism being that they don't 'soft start' particularly well with some LEDs but then I haven't really found a dimmer that does.
 
What you say is correct, but using the technology suggested, the momentary 'on' from the switch operates the control circuitry, which then turns on/off the light appropriately.
In the case of Quinetic remote switches, the mechanical push 'pings' a piezo electric generator, which creates power for a small rf transmitter that sends a signal to the receiver in the light circuit.
I was a little dubious about this system but ordered a two way set for my father in laws garage and they are simply magical I also wondered about the no battery but your right just like the lighters they work a dream ! The switches I got were round tho and so don’t look like any light switch you find but I’m sure there will be ones out there that would look right !
 

Reply to One touch light switches in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
621
Hi all, Hopefully just a quick one, but I can't seem to find a definite answer. Will a push to break/make (ie not momentary) 2 way retractive...
Replies
7
Views
820
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
543
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock