Discuss Ongoing storage heater problems - some help would be much appreciated. in the UK Electrical Forum area at ElectriciansForums.net

jedisparks

-
Arms
Reaction score
76
Have an on going problem with a storage heater (Dimplex CXL24N). I've been out to look at it 3 times now and the occupier says that it still isn't working properly.

I was originally called out to it because it didn't work. The thermal reset had gone (not uncommon) and the thermostat did not look in good shape, So I ordered a new one and fitted it (2nd visit). During this call I had all the elements out to take a look and test resistance and IR. They all had similar resistance accross the elements.

Then I got called back becasue the heater wasn't getting hot enough and on attending I agreed and would have expected it to be a bit hotter than it was. So I wondered if one of the elements had gone. However on feeling the front of the heater It didn't feel like one area was cooler than the rest. Also, the resistance accross the whole heater was 17.8 ohms which I figure to be about right. 240/17.8 = 13.48Amps, 240 x 13.48 = 3.2KW. So, for a 3.4KW heater that seems about right...??

Anyway had another call today to say that it still isn't right and I don't really know where to go next. I'm doing this for a landlord, in one of his rentals. So far I've attended 3 times and paid for a new stat but can't really charge him if I haven't fixed anything. Here is a list of what I have checked, have I missed anything?:

1) Stat - replaced with a new one
2) thermal cutout - reset
3) Elements - removed, examined for damage, continuity and IR tests satifactory
4) Isolator wall switch - Replaced as I did find a high resistance accross the neutral terminals
5) Checked continuity of supply cables from consumer unit - checked out fine
6) Got rid of all the dust inside the heater
7) Asked if they dry clothes on the heater - Occupier says no, but sometimes puts their socks on the back, not covering the air vent (I'm a bit suspicious of this but it doesn't explain what's going on).
8) Is it the time clock - the clock is inaccessible. However there is another heater in the flat which is working fine.
9) Checked resistance accross the whole heater from the isolator switch (in the off position) got a reading of 17.8 ohms
10) Fuse protecting the circuit checked out fine
11) Continuity from the busbar to the outgoing terminals on the fuse holder tested fine.

Basically, I'm stumped. any ideas?

Thank you.
 
Its been a while since I've done any work on storage heaters but yes they can fail and cause the problems you are having, I would replace that and see if it makes a difference. Good luck

A good call from 44ALLAN also.
 
Ok thanks, The existing one isn't touching any bricks or hotspots, so replacing that could be the next step.

I did wonder whether it might be worth replacing the accelerator unit too, but not sure if these go wrong either.

I've been fiddling with storage heaters for years and it's usually been thermostat, cut out, elements, isolator siwtch, or fuse. So, this is a new problem for me.
 
Here is a method that works for me.
Get a length of flex attach it to the removed faceplate
Plug into nearest socket. Get clamp meter and stick on neutral of flex
Operate charge control to see if it's working correctly it will flash if it is
Check load which for a 24 will be between 12 and 14 amp.
This method checks the elements charge control and switch in a five minute operation
Least it's a dimplex unlike the creda I had to fix yesterday gash it was
 
When you say the accelerator unit, that maybe what I call the charger unit which located at the top by the switches etc. We generally changed that with the capillary as a job lot. Didnt have many problems after that. When ever I carried out repairs with heaters it was very rarely anything else other than the charger/capillary or stat, on occassions resetting the cutout when people drying clothes on them. Hope this helps.
 
Thanks Dcf, Yes I will try that. When you say 'flash', I take it you mean a small flash when you turn the stat on, as it contacts?

What do you think about the capilliary thing?

thanks again
 

Reply to Ongoing storage heater problems - some help would be much appreciated. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
803
There was always talk of teleswitch transmitters being switched off. Does anyone know if that is a thing, or whether it’s been done? I was at a...
Replies
9
Views
1K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Hi, I have a customer with a Storad SR140-3 storage heater (in the bathroom), which does not work. The resistance of the elements is ok. There...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock