I was sent to do a EICR on a DB in a commercial kitchen and could do with some opinions on which codes to give. seeing as I haven't done a EICR since the spring and only doing new installation certs I have a fair idea but feel a bit out of confidence with it.

thanks in advance for your input:


1 - cables from the DB not in CMS or sufficiently supported
2 - outer sheath on T&E cables stripped back outside of DB
3 - no blank covers on DB
4 - no busbar cover
5 - no rcd protection on socket outlets
6 - 4 cables terminated into one of the MCBs
7 - different ill fitting MCBs in DB
8 - 20mm holes in DB

thats all i can think of off the top of my head, im sure theres more if i'm back there tomorrow il upload a picture it looks rough!

i'd say

1 - c3
2 - c2
3 - c1
4 - c2
5 - c2
6 - c3/FI
7 - c3
8 - c2

??
 
1) Code C2.
2) Code C2.
3) Code C1.
4) Code C2.
5) No code, unless they are intended for unsupervised use by customers, in which case code C3.
6) No code.
7) Code C2.
 
The sockets in r5 are on a food prep bench area where they use hand held mixers etc and near to a sink surely they should be 30mA protected?
 
Sockets for use by 'ordinary' persons intended for general use are required to be RCD protected.....an exception is permitted for sockets under supervision of skilled or instructed persons.....411.3.3.
Debatable whether cooks are skilled or instructed persons when it comes to the safe use of sockets in a potentially wet area.....I would code 3.
 
Regulation 16 from the EAWR:
"Persons to be competent to prevent danger and injury
16. No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work."

This requirement from the EAWR means that anyone, whether they be a cook, cleaner, secratary or whatever, must be so experienced, trained, qualified or under such supervision so as to satisfy the BS7671 definition of a 'skilled' or 'instructed' person.
The EAWR is a statutory requirement, if it is not complied with, the law is being broked.
BS7671 does not make Regulations for instances where the law is being broken.
I think the premis is, that if someone is not going to comply with the law of the land, they are hardly going to comply with a non-statutory set of Regulations such as BS7671.
 
And so nearly every person would be classed as a skilled or instructed person and the regulation would be no use...

I dont believe this is the way the regulation is to be interpreted...

The people imo aren't skilled or instructed persons and so requires RCD protection...

The 20mm holes, does this leave access to live parts?...are they empty holes that need blanks?...

Sent from my Xperia S using next doors WIFI
 
Obviously, you can interpret the Regulations however you wish.
If you wish to interpret them incorrectly, that is your choice.

The fact remains, that there are a number of statutory requirements that apply to employees, their employers and even the self employed.
There are no statutory requirements that apply to 'ordinary' persons in domestic installations.

The BS7671 definition of a 'skilled' person is: "A person with technical knowledge or sufficient experience to enable him/her to avoid dangers which electricity may create."
In other words, sufficient technical knowledge orsufficient experience to know not to drill or hammer a nail into into a wall just above a socket-outlet without first checking that there are no concealled cables where they are about to drill or hammer a nail.
In other words, sufficient technical knowledge or sufficient experience to know not to use an item of equipment or lead that is damaged.
In other words, straight out of Regulation 16 of the EAWR: "No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience,"

The BS7671 definition of an 'instructed' person is: "A person adequately advised or supervised by skilled persons to enable him/her to avoid dangers which electricity may create."
In other words, adequately advised or supervised by skilled persons to enable him/her not to drill or hammer a nail into a wall above a socket-outlet without first checking that there are no concealled cables where they are about to drill or hammer a nail.
In other words, adequately advised or supervised by skilled persons to enable him/her to know not to use an item of equipment or lead that is damaged.
In other words, straight out of Regulation 16 of the EAWR: "or is under such degree of supervision as may be appropriate having regard to the nature of the work."

Now you as the inspector, can decide that the cook, cleaner, secretary or whatever does not have the technical knowledge or experience necessary to prevent danger, or where appropriate, injury.
You can decide that they are not under such degree of supervision as may be appropriate having regard to the nature of the work.
You can decide that your client is breaking the law, is in fact a criminal.
You can if you so decide, issue a document defaming your client.
However, I would suggest that before you do so, that you consider the wording of Regulation 16 of the EAWR, the wording of Regulation 411.3 and the wording of the definitions for 'skilled' and 'instructed' persons.

Do not fall foul of the common misconception that a skilled person must a qualified electrician, or that an instructed person must be an electrician's aprentice.
The definitions in BS7671 do not bear out the misconception.
 
Despite Spins spactacularly comprehensve answer above....:tt1:....the fact that this is a food prep area and may involve water means (IMO) that instructed person or otherwise a hazard exists which warrents RCD protection and hence a code.(3 IMO).
Completely accept though that the whole thing is open to interpretation.
 
According to the niceic its someone with electrical training

Id C3 you can sleep easier its up to the customer whether they get remedial work done so the buck passes to them
 

Reply to opinions/ advice on which codes to give on EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
650
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
917
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
5K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock