Discuss Opinions sought please in the Australia area at ElectriciansForums.net

E

electricAl

http://www.electriciansforums.net/attachment.php?attachmentid=1432&stc=1&d=1276614122

Installation is in a large, period domestic dwelling. Property rewired 2007. The final ccts for the main house are supplied by the 16th Ed. split-load CU seen at the top of the pic, with Max demand for the main house reasonably assessed as not too far off the 100a mark.
The 3 phase supply was installed last year - it was suggested by the installer, in order to supply a dedicated sub-main to an annexed cottage. The cottage has it`s own D/B, with a 30mA RCCB incomer supplying B32`s for cooker & rfc, and B6 lighting circuits (x2). Extraneous-conductive (water service in metallic pipework) parts in evidence thru-out the cottage.

For clarity, the new dist.cct for the cottage has actually been supplied from the 30mA RCD protected side of the main board, running in 10mm T&E from a B50 to the 3 Henleys . As can be seen, its fed from there into 3 core 16mm XLPE which drops (with no further support) the 2m to the concrete floor.
It then terminates into an external 300x300x150 insulated enclosure on an external wall, and connects to an outgoing SWA (same 3c x 16mm) via Weidmuller type disconnect terminals. These DIN rail terminals are in free air within the box, held in position simply by the cores attached to them. No end plates are fitted.
Correct CW25 glands are fitted to each of the 2 SWAs at this box, but no banjo`s, and no other means to achieve continuity between the armour of each sheath. The entry hole for one has been drilled into the reinforcing ribs, so the galv backnut can`t be tightened flush.
Termination at the cottage`s CU is unclear. The supply 3c X16mm cores eventually re-appear close to the all insulated D/B, but the armour, inner & outer sheaths, are all hidden within the partition wall.

I`ll say nothing more at this stage, other than to invite your comments. At some point soon i`ll be in a better position to explain more fully.
 

Attachments

  • What the.jpg
    108.5 KB · Views: 127
Last edited by a moderator:
No pics Al
Sorry just popped up ,must be my slow connection.
If an electrician did that,I hope hes ashamed of himself.
 
Last edited:
3-phase metering-only 1 phase in use

sub-main not glanded supply side

sub-main taken from rcd side of main board-a major discrimination cock-up


are they converting to TT or exporting the earth to the cottage-afraid i'm only getting to grips with UK rules
 
Looks to me like an installation that has not been finished off and the armoured was temporarly terminated pending installation of the three phase

It's the only reason I can think of for only using one phase
 
Your logic is sound, but sadly, that wasn`t the timeline of the work. New header installed first (14 months ago) then the sub-main soon after.

Furthermore, i`d like to think decent sparks would be uncomfortable leaving this even overnight
 
The termination of the SWA is unacceptable and if the TNCS earth is exported to the cottage extraneous parts within the cottage must be bonded back to the MET at the intake....there is no evidence of that.
 
the SWA not having a gland is a NONO and using the black as neutral and grey as earth is "Bad practice" the it would be better to gland into a box and join inside
 
Defo looks like someone ran away with the money half way through the job. Looks like they just needed a temporary supply to the cottage to do some work and called it a day. Looking at the way the SWA has been "prepared" there is no way that was intended to be terminated properly. V poor IMHO :(. Any ideas what the other two blocks were destined for?
 
using the black as neutral and grey as earth is "Bad practice"

Can't agree with that. So long as they are corectly reidentified then there is no difference either way. That's just the NICEIC's opinion on the matter. There is no regulatory basis and I cannot see how it is any worse practice.
 
It looks to me like the original distribution board may have been adjascent to the supply head

A new consumer unit fitted (the swa now being too short to reach the new consumer unit position)
The installers or other, then adapting what was left to get a supply to the swa in some sort of fashion

A naughty temporary becoming a permenent and extra naughty danger and eysesore
 
Welcome back Al.

Thought you had gone AWOL.

I did

But the plumbing idea was flawed :eek:

Seriously tho, nice to be on here again with you lot of scally`s



As to starting this thread... Apologies for being rather mysterious, but i respect the opinion of many of you fellas and was hoping you`d offer a unbiased opinion as to the standard, or otherwise, of this install. When i`m able, i`ll share the reasons why this particular job is more insiduous than the all too common mess left by a cowboy.
Afraid the world weary way in which Lenny replied probably strikes a chord with many of us - " its only averagely cr4p, nothing outstanding"
 
Dont know if my comment came across the way I meant it too.:eek:

My thoughts were only that while the majority of us pay our fees and try our bloody hardest to do the job the way we all know it should be done, you'll always get the "bill form the pub" types who may very well have their own electrical companies with 20 vans but still dont give a rats hoop about the job they do.

Taking a bit of pride in what you do obviously isn't for everyone, but abiding by ol'red is to all.;):)
 

Reply to Opinions sought please in the Australia area at ElectriciansForums.net

Similar Threads

Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K
Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
Replies
42
Views
6K
Apologies for the complexity of this question, but thereā€™s no easy way to explain it. This is a remote Norfolk house and workshops, developed...
Replies
12
Views
2K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
T
Morning all. I'm after some suggestions please - I'm at the very early stages of a new build for a customer and just planning ahead for getting...
Replies
51
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock