Search for tools and product advice,

Discuss Outdoor lighting and out house cabling in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi guys

Garden is around 100ft long and I am looking to build a small out house at the back of it. I would also like landcape lighting throughout the garden.
Would you guys run seperate cables from the main house i.e
1)one for outhouse and other for landscape lighting
or
2) would you run one to outhouse (for lighting and power) and from the outhouse run out the landscaping cables?

Also what swa cable size would I best use for a small 4 way board to run from house to back of garden 100ft away?

Also if I was to choose option 1 would I be ok in running the landscape lighting from an fcu off a ring main from the main house with such a decent cable run around the garden.

Many thanks for your help
 
Do you have a sketch of the layout of where things are going?
 
The type of control used to be a big factor

PIR/timer you can wire from shed if convenient

Switching from house would mean separate wiring from house

Probably not the case anymore.with quinetics ,claimed 80m range outdoors,I'm not familiar with them

If quinetics are a game-changer now it will usually be simpler to wire from shed if you're laying cabling round the perimeter of the garden
 
Last edited:
Just general spike lights and uplighters throughout the borders for the landscape lighting, around 30 in total. Doubt it will be more than 500w in total.
And the outhouse will only be a handful of double sockets with a lighting circuit. A garage consumer unit will likely be ample I'd have thought.

Would you have and idea on what size cable for the meter tails would I need for the outhouse?
 
Yes…but…I have seen what has been described as “outhouses” that are effectively small houses


What will be plugged in to the sockets?
MIG welder
3kW heaters
Water heater
Tumble dryer
Granny charger for EV
Future plans

100ft is a long way if there is even one substantial load
 
Yes…but…I have seen what has been described as “outhouses” that are effectively small houses


What will be plugged in to the sockets?
MIG welder
3kW heaters
Water heater
Tumble dryer
Granny charger for EV
Future plans

100ft is a long way if there is even one substantial load
Just the likes of a fridge and TV appliances.
What would you recommend I best do? There are a couple of spare ways in the main house consumer unit but like I say your talking the back of the garden from CU is 150ft away.

What is the usual way to attack this situation?
 
As already mentioned, any new circuit is notifiable under part P of the building regulations in England and Wales, you really are best to get in a registered electrician to sort this out.

Once the design is agreed and a cable chosen by the sparky, they will often be quite happy for you to do the donkey work of trenching the cable to save some money.

You don't have to bury cable, it could be run around a fence/wall if adequately supported and protected from any likely damage, but burying a length of armoured cable is common. However, better still is to bury some twinwall duct to allow cable to be pulled though along with any network cable, etc, you might need.

Knowing the max load is critical to the cable choice. So think about it very carefully before you start as the extra cost to put in larger at the start is far less than replacing something inadequate later. However, there are some other aspects like earth-bonding of anything like metallic water pipes that can be a factor as well in sizing things.
 

Reply to Outdoor lighting and out house cabling in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Replies
30
Views
595
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
699
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
851
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock