Discuss Outside light RCD protection in the Lighting Forum area at ElectriciansForums.net

For those of you who want to drag up the definition of a DB/CU, and say that an FCU is a DB/CU.
Just remember Regulation 421.1.201:
“Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.”
Spin, You are probably correct and I respect that you have spent a bit of time researching this regulation.
All I did was brought up the definition of "Circuit" never once did I say an RCD FCU was a DB or CU so I dont see why it would it need to bound to same constraints ?

I was just looking at Regulation 411.3.4 and your right !! The difference between this regulation and 411.3.3 which covers socket outlets is the part.. "provided for AC final circuits"

Thats why I posted the definition on circuit, it wasnt to be akward or disagree, I was also always taught when putting a FCU on a final circuit then you are changing the characteristics of the addition so the circuit starts from the point where the overcurrent protective device changes, and ive occasionally put a Sw fcu with a 3amp fuse on a rfc to supply a light in a cupboard, as Ive been using logic.
 
Interesting discussion, I've not got the BBB nor had any training etc on the 18th.

Previously I sort guidance on reg 701.411.3.3, and was advised that the protection of low voltage circuits serving locations (bathrooms etc), would be compliant utilising a local RCD FCU.

Albeit I take spinlondon's point of definition of circuit. However that definition does say '....protected against overcurrent by the same protective device'.

With regard 411.3.4, if I replaced a ceiling rose with a new luminaire, or re-terminated the fixed wiring with a jb of some sort, and extending the wiring with additional cabling, then the existing circuit would now need additional protection at the origin to comply? Or as in this case, additional fixed wiring, would also been at the origin and not locally as above.

I think I would need to seek some guidance on this point. Otherwise in a domestic environment, I could see sparks losing a lot of work, if this is the case.
 

Reply to Outside light RCD protection in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
354
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Replies
8
Views
420
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
692
Hi all, I have a single switch in my garage to turn on a couple of lights in there. Yesterday I fitted a floodlight outside, drilled through...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock