I have just been asked by a customer if he can just plug his new cooker into a socket. I have said 'No' it needs to be on a dedicated circuit..
I then thought I'd do a bit of research as its only a 2.5kW oven and wanted to see it in black and white in the regs.
I didn't ecpect the Electricians Guide to the Building Regulations (Page 55 - 4.4) to say
"For lightly loaded circuits ovens of rating 13A or less may be connected into a ring final circuit"
Not sure if his kitchen is on its own ring, but if it is I guess its ok to plug in the oven?
Just doesn't seem right, especially after seeing all of Jason's entrys about having to be 2kW or less?
ps... I'll make this my last post for a bit, getting a bit carried away and a bit addicted to this electrics lark ...:rolleyes4: