I have just been asked by a customer if he can just plug his new cooker into a socket. I have said 'No' it needs to be on a dedicated circuit..

I then thought I'd do a bit of research as its only a 2.5kW oven and wanted to see it in black and white in the regs.

I didn't ecpect the Electricians Guide to the Building Regulations (Page 55 - 4.4) to say

"For lightly loaded circuits ovens of rating 13A or less may be connected into a ring final circuit"

Not sure if his kitchen is on its own ring, but if it is I guess its ok to plug in the oven?

Just doesn't seem right, especially after seeing all of Jason's entrys about having to be 2kW or less?

ps... I'll make this my last post for a bit, getting a bit carried away and a bit addicted to this electrics lark ...:rolleyes4:
 
if it comes with a fitted plug, then it's OK to plug it in.
 
The dedicated circuit issue mainly revolves around loads of a constant deman, such as the immersion.

If it is a domestic appliance used irregularly then it makes little difference.
 
If there an unused cooker outlet you could change it for a single socket and plug the oven into that,then you will have a dedicated circuit and the customer can use the existing cooker switch to turn it on and off if they so wish.
 
New posts

Reply to Oven connected into ring - EGBR says this is ok? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I've got a new oven and have a question about installing it. It's a 2.6kW 13A oven, and a cable from the 32A cooker circuit to...
Replies
4
Views
301
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
I am replacing my under counter oven with a new 3kw one, oven is on its own circuit and isolation oven switch, the cable is either 4 or 6mm coming...
Replies
7
Views
1K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
796
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
237

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock