Discuss Oven Replacement - RCD? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
326
Afternoon all. Apologies if this is a stupid question. I'm currently half part way through completing 2391 (second exam tonight) - so may be getting myself in a tiz overthinking things.

Either way, thought I'd put it out to the group.

Task is: Straight swap of existing x5 ovens with new - "like for like", if you will. Albeit cooker plate to appliance is also in T&E and I intend to replace this with a more suitable product - namely HO7.

Earthing arrangement is: TN-S.

Environment is: Educational establishment, cookery rooms.

Circuits for the room originate in a local 3P+E MEM2 board, no RCD's. Ovens are simply domestic 1P+E bog standard, cheap household jobs, wired from C32's at the DB to 45a Isolators (no socket) at each station, cooker outlet below. Room is only about 10m long.

EICR from 2020 is available, but quite a few tests missed out - IE: Zs for each oven measured well within limit. No IR or R1+R2 undertaken - I'll be doing this anyway. It's all PVC T&E - mainly in metal trunking. I think it's loose behind the cabinets for the last few metres however.

My big question here is RCD. I could take the "like for like" approach and just straight swap the ovens out as "maintenance". But the environment (education) makes me think I really should be pushing for RCD's.

Further to this, manufacturers instructions state "Additional protection by RCD is recommended".

With that in mind, I'm convincing myself these really should be going onto RCD shouldn't they?

Or convince me I'm wrong. Sorry if I've overcomplicated a simple job here.

Thanks.
 
Afternoon all. Apologies if this is a stupid question. I'm currently half part way through completing 2391 (second exam tonight) - so may be getting myself in a tiz overthinking things.

Either way, thought I'd put it out to the group.

Task is: Straight swap of existing x5 ovens with new - "like for like", if you will. Albeit cooker plate to appliance is also in T&E and I intend to replace this with a more suitable product - namely HO7.

Earthing arrangement is: TN-S.

Environment is: Educational establishment, cookery rooms.

Circuits for the room originate in a local 3P+E MEM2 board, no RCD's. Ovens are simply domestic 1P+E bog standard, cheap household jobs, wired from C32's at the DB to 45a Isolators (no socket) at each station, cooker outlet below. Room is only about 10m long.

EICR from 2020 is available, but quite a few tests missed out - IE: Zs for each oven measured well within limit. No IR or R1+R2 undertaken - I'll be doing this anyway. It's all PVC T&E - mainly in metal trunking. I think it's loose behind the cabinets for the last few metres however.

My big question here is RCD. I could take the "like for like" approach and just straight swap the ovens out as "maintenance". But the environment (education) makes me think I really should be pushing for RCD's.

Further to this, manufacturers instructions state "Additional protection by RCD is recommended".

With that in mind, I'm convincing myself these really should be going onto RCD shouldn't they?

Or convince me I'm wrong. Sorry if I've overcomplicated a simple job here.

Thanks.
This is a commercial install. No 30mA protection need as long as all the bonding is as it should be.
 
The fact it is a school does not enforce the requirement for rcd protection. The fly in the ointment is the manufacturer 'recommending' rcd protection so read that as you will, recommending does not necessarily insist on it being done. Provided the existing devices satisfy ADS then to me it is fine.
 
The fact it is a school does not enforce the requirement for rcd protection. The fly in the ointment is the manufacturer 'recommending' rcd protection so read that as you will, recommending does not necessarily insist on it being done. Provided the existing devices satisfy ADS then to me it is fine.
Yes, that does make sense. The reccomendation is indeed the main point that was bothering me. I suppose the theory behind this is to put the onus back on the installer.
 
I would be very careful with the word 'recommended' right now... my understanding is that amendment 2 introduces a handy definition which implies "recommended" = "should". This has come to my attention specifically in relation to the installation of arc fault detection devices, but it's not beyond the realms of possibility that all recommendations are now must do's.
 
The BSI have taken a common, well defined word, that everyone understood perfectly from an early age, and re-defined it to something that doesn't tally with the dictionary definition, so now we're all confused about it. If they mean 'should' then why not use the word should.

I would suggest it's the manufacturers sitting on the various committees that are driving things these days. Feels like things are changing just to sell more gear. I've got a situation at the moment where if I comply fully with the regs, a consumer unit that would cost £240 (this is for a BG board - only one that will fit with SPD and RCBOs) is going to cost well in the region of £850 because there are four socket circuits. I could potentially reduce that to maybe £550 by connecting three (old radial heater supplies with a single socket on each) of them together but overall, it's a ridiculous situation so now I'm thinking of having the client decline the AFDD option and record it as a departure. This is one bed cottage that needs a satisfactory EICR to comply with the Welsh rental laws. Currently two 3036 boards, everything is spot on apart from a socket outlet with a cracked face and rotting backbox... except it has no additional protection (has a 100mA upfront - TT earthing).

Recommended means you should really, but it's still optional.

As you say, they've redefined a word... still... that seems to be the game everyone is playing these days ;)
 
I would suggest it's the manufacturers sitting on the various committees that are driving things these days. Feels like things are changing just to sell more gear. I've got a situation at the moment where if I comply fully with the regs, a consumer unit that would cost £240 (this is for a BG board - only one that will fit with SPD and RCBOs) is going to cost well in the region of £850 because there are four socket circuits. I could potentially reduce that to maybe £550 by connecting three (old radial heater supplies with a single socket on each) of them together but overall, it's a ridiculous situation so now I'm thinking of having the client decline the AFDD option and record it as a departure. This is one bed cottage that needs a satisfactory EICR to comply with the Welsh rental laws. Currently two 3036 boards, everything is spot on apart from a socket outlet with a cracked face and rotting backbox... except it has no additional protection (has a 100mA upfront - TT earthing).

Recommended means you should really, but it's still optional.

As you say, they've redefined a word... still... that seems to be the game everyone is playing these days ;)
Is not having an AFDD a departure? And you could you fit an SPD in a separate unit before the boad? Or get them to sign saying they understand they should have it but do not won't it.
 
Is not having an AFDD a departure? And you could you fit an SPD in a separate unit before the boad? Or get them to sign saying they understand they should have it but do not won't it.

I would say absolutely 100%, if you don't install AFDDs where they are required it's a departure and as I've outlined above, the regulations and the definition of "recommended" mean they are required in all domestic settings.

But that's just my interpretation, I'd be more than happy to be proven wrong.
 
I would say absolutely 100%, if you don't install AFDDs where they are required it's a departure and as I've outlined above, the regulations and the definition of "recommended" mean they are required in all domestic settings.

But that's just my interpretation, I'd be more than happy to be proven wrong.
Go back through the new regs. SPDs a must or wavier. AFDDs still just a bog standard recommendation with no caveat.
 
I don't have the BBB yet, but if this is what the regs actually say...

"Regulation 421.1.7 now states:

Arc fault detection devices (AFDD) conforming to
BS EN 62606 shall be provided for single-phase
AC final circuits supplying socket-outlets with a rated
current not exceeding 32 A in:

• Higher Risk Residential Buildings (HRRB)
• Houses in Multiple Occupation (HMO) i
• Purpose-built student accommodation ii
• Care homes iii

NOTE 1: Higher Risk Residential Buildings are assumed to
be residential buildings over 18 m in height or in excess of
six storeys, whichever is met first. It is anticipated that in
many areas higher risk residential buildings will be defined in
legislation which can be subject to change over time, as well
as in risk management procedures adopted by fire and rescue
services. Current legislation should be applied.

For all other premises, the use of AFDDs conforming
to BS EN 62606 is recommended for single-phase
AC final circuits supplying socket-outlets not
exceeding 32 A.


Where used, AFDDs shall be placed at the origin
of the circuit to be protected.
The use of AFDDs does not obviate the need to apply
one or more measures provided in other clauses in
BS 7671.

NOTE 2: For busbar systems conforming to BS EN 61439-6
and Powertrack systems to BS EN 61534, the AFDD may be
placed at a location other than the origin of the circuit."

Thats taken from this:-


Which also clarifies the "recommended = should".

I'd say there's no room for a choice in there.
 
So your saying all new installations, DB changes you have to install AFDDs. EICRs, what code 2/3. Your wrong. Not mandatory.
No I'm not saying that.
Read 421.1.7
Note the word "shall".
Your original generalisation was not true.
What you guessed I was saying is also not true.
 
I don't have the BBB yet, but if this is what the regs actually say...

"Regulation 421.1.7 now states:

Arc fault detection devices (AFDD) conforming to
BS EN 62606 shall be provided for single-phase
AC final circuits supplying socket-outlets with a rated
current not exceeding 32 A in:

• Higher Risk Residential Buildings (HRRB)
• Houses in Multiple Occupation (HMO) i
• Purpose-built student accommodation ii
• Care homes iii

NOTE 1: Higher Risk Residential Buildings are assumed to
be residential buildings over 18 m in height or in excess of
six storeys, whichever is met first. It is anticipated that in
many areas higher risk residential buildings will be defined in
legislation which can be subject to change over time, as well
as in risk management procedures adopted by fire and rescue
services. Current legislation should be applied.

For all other premises, the use of AFDDs conforming
to BS EN 62606 is recommended for single-phase
AC final circuits supplying socket-outlets not
exceeding 32 A.


Where used, AFDDs shall be placed at the origin
of the circuit to be protected.
The use of AFDDs does not obviate the need to apply
one or more measures provided in other clauses in
BS 7671.

NOTE 2: For busbar systems conforming to BS EN 61439-6
and Powertrack systems to BS EN 61534, the AFDD may be
placed at a location other than the origin of the circuit."

Thats taken from this:-


Which also clarifies the "recommended = should".

I'd say there's no room for a choice in there.
Wow. Sorry dude. Need to look more into that. Need to see if we're just looking at new builds. And 18m is pretty high. I do mainly EICRS so need to see where this sits. Again, apologie🙏
 
Which also clarifies the "recommended = should".
I would take that clarification with a ton of salt.

Page 18 of the new regs book has a little table. The 2nd column should be the first column, as the intent is to translate the verbal form in BS7671 to an implication.
It says "Shall" is a requirement and normative, and "Should" is a recommendation (and is not normative)

If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

There is a misleading view being communicated within the industry that use of such terms as ‘recommended’, ‘additional’ and ‘specified’ demotes the requirements within the associated regulations.

In particular, Recommendation is ONE possibility and does not exclude other possibilities (including doing nothing)
 
If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

I suspect if one's interests were heavily invested in the sale of associated goods, then it would be very easy to reach such a conclusion.

Is a trade association wilfully misrepresenting BS7671? I couldn't possibly speculate.
 
I would take that clarification with a ton of salt.

Page 18 of the new regs book has a little table. The 2nd column should be the first column, as the intent is to translate the verbal form in BS7671 to an implication.
It says "Shall" is a requirement and normative, and "Should" is a recommendation (and is not normative)

If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

There is a misleading view being communicated within the industry that use of such terms as ‘recommended’, ‘additional’ and ‘specified’ demotes the requirements within the associated regulations.

In particular, Recommendation is ONE possibility and does not exclude other possibilities (including doing nothing)

Excellent! I knew I'd seen that somewhere
It has to be the case, otherwise the requirements for where AFDDs are fitted wouldn't make sense in the way they are split.
 
I would take that clarification with a ton of salt.

Page 18 of the new regs book has a little table. The 2nd column should be the first column, as the intent is to translate the verbal form in BS7671 to an implication.
It says "Shall" is a requirement and normative, and "Should" is a recommendation (and is not normative)

If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

There is a misleading view being communicated within the industry that use of such terms as ‘recommended’, ‘additional’ and ‘specified’ demotes the requirements within the associated regulations.

In particular, Recommendation is ONE possibility and does not exclude other possibilities (including doing nothing)
Nice one Tim! So it's the word 'should' that has been defined, rather than the word 'recommend'? Ok, now it's starting to make sense! 👍
 
Nice one Tim! So it's the word 'should' that has been defined, rather than the word 'recommend'? Ok, now it's starting to make sense! 👍
The more you look into this, the more daft it gets.
Here's the table in BS7671:
1668715333841.png


Note the bit at the bottom.
Now, if we look at that joyous publication, it contains this table, the ancestor.
1668715389250.png


For a completely inexplicable reason some nitwit thought it made sense to invert the first two columns in BS7671. The only bit that adds clarity is that "Should" is always "Informative" in BS7671.

The BSI document also says:
1668715622639.png


So yes, the only way this makes any sense is if "should" is the thing being defined, which is how the drafting standard which BS7671 aspires to comply with has it.
 

Attachments

  • 1668715531693.png
    37.8 KB · Views: 2
I'm employed directly by the organisation. Not a contractor, actual payroll. I've spent 3 nights thinking about this. Going by my salary thats over £345 worth of thinking hours. I proceeded to buy £360 of MR30 pods from Willrose in the end. I slept better for it. (Cue the argument about fitting used goods. They come tested, I retested them and all was fine and noted it on the cert. What more can you do other than replace an entire board). Ultimately as above, it's a bit of a **** situation on BSI's part. But I've gone above and beyond in making it safer than I found it if nothing else.
 
I'm employed directly by the organisation. Not a contractor, actual payroll. I've spent 3 nights thinking about this. Going by my salary thats over £345 worth of thinking hours. I proceeded to buy £360 of MR30 pods from Willrose in the end. I slept better for it. (Cue the argument about fitting used goods. They come tested, I retested them and all was fine and noted it on the cert. What more can you do other than replace an entire board). Ultimately as above, it's a bit of a **** situation on BSI's part. But I've gone above and beyond in making it safer than I found it if nothing else.
You have followed the manufacturers recommendation, and no one could/shall/should (!) shoot you down for doing so!
 
So thinking above oven elements….and I’m definitely over thinking here….
An rcd tripping is fairly common if an element is on its way out.
If the failure mode is leakage to earth, is it fair to assume that if there was no RCD this could degrade over time, and the fault resistance could get low enough to make the cooker a bit tingly to the touch but not super-low enough to trip an over current device.
Or does it tend to end up open circuit before that happens?
I’m just wondering how this played out before we had RCDs.
 
So thinking above oven elements….and I’m definitely over thinking here….
An rcd tripping is fairly common if an element is on its way out.
If the failure mode is leakage to earth, is it fair to assume that if there was no RCD this could degrade over time, and the fault resistance could get low enough to make the cooker a bit tingly to the touch but not super-low enough to trip an over current device.
Or does it tend to end up open circuit before that happens?
I’m just wondering how this played out before we had RCDs.
I can't think of one that I've seen that was tripping breaker/fuse.
I guess it depends on where the element fails and if that element touches the casing.
 
I am a specifier, who employs electricians, and I am familiar with the regs. My actual background is lawyer. Perhaps professionals are looking at this (including AFDDs) the wrong way.

What I say to myself is "the manufacturer has recommended this, it is also strongly advised (at the least) in the regulations, therefore best practice and the most defensible position is to fit the device". If for any reason there is an accident or fire, the judge would want to know precisely why you ignored recommendations or regulatory guidance, and how you communicated and documented that, and how you mitigated the risks. If ever it got to court, you could be certain that the other side (insurance company barrister probably) would have an expert on hand to say that failure to follow recommendations is negligent. They would pay little heed to semantic discussions along the lines of "recommended means optional".

In our developments we fit AFDDs to socket circuits now as a matter of course, and in the example above where these are domestic ovens with an explicit manufactured recommendation of an RCD, I would specify that too. It is much better to do this than have to mount some defence later and try to convince a court that I know better than the manufacturer of the product.

Extra cost is peanuts in the context of a development or commercial installation. I accept that domestic remedial installers may have an uphill task getting people to accept the extra costs though.
 
I can't think of one that I've seen that was tripping breaker/fuse.
I guess it depends on where the element fails and if that element touches the casing.
So thinking above oven elements….and I’m definitely over thinking here….
An rcd tripping is fairly common if an element is on its way out.
If the failure mode is leakage to earth, is it fair to assume that if there was no RCD this could degrade over time, and the fault resistance could get low enough to make the cooker a bit tingly to the touch but not super-low enough to trip an over current device.
Or does it tend to end up open circuit before that happens?
I’m just wondering how this played out before we had RCDs.
When an element fails it is a dead short. Usually all three are down. Doesn't matter if its an emersion kettles, oven or any other element when they finally go it'd a dead short and the MCB,fuse,rcbo will trip. Most elements under 18 mega ohm will start tripping the protective device. I know some people will question that and yes your right it depends on the wattage of the element but in most domestic and commercial situations this is the fact.
 
When an element fails it is a dead short. Usually all three are down. Doesn't matter if its an emersion kettles, oven or any other element when they finally go it'd a dead short and the MCB,fuse,rcbo will trip. Most elements under 18 mega ohm will start tripping the protective device. I know some people will question that and yes your right it depends on the wattage of the element but in most domestic and commercial situations this is the fact.
And if the fault is between L&N then the RCD shouldn't be tripping first.
 
When an element fails it is a dead short. Usually all three are down. Doesn't matter if its an emersion kettles, oven or any other element
I have never seen a wire wound fire element go short, in fact, I don't think it's even possible as the heater element goes open in a failer and being as there is no earthed casing to contact it just sits there not working.
Most elements under 18 mega ohm will start tripping the protective device.
An 18 mega ohm element will trip ?????

That's around 0.0000127777778 amps, or 0.00293888889 watts.




and yes your right it depends on the wattage of the element but in most domestic and commercial situations this is the fact.
Nobody mentioned wattage.

When an element fails it will usually "open" the electrical circuit and no further heating will take place. When this happens, the element simply appears to have stopped working.In some rare instances the element will "short-out" against the sheath which is the outer visible part of the surface unit.
 
Last edited:
I have never seen a wire wound fire element go short, in fact, I don't think it's even possible as the heater element goes open in a failer and being as there is no earthed casing to contact it just sits there not working.

An 18 mega ohm element will trip ?????

That's around 0.0000127777778 amps, or 0.00293888889 watts.





Nobody mentioned wattage.

When an element fails it will usually "open" the electrical circuit and no further heating will take place. When this happens, the element simply appears to have stopped working.In some rare instances the element will "short-out" against the sheath which is the outer visible part of the surface unit.
I've been to numerous faults where the cooker circuit has tripped and will not reset. And the issue has always been the element. Same as 3kW emersion. Yes 18mw starts to nuisance trip. Don't know why this happens but it seems to.
 
Let's keep this discussion civil gents!
I've certainly known elements that are measuring respectable values when cold but will trip an RCD when energised after a minute or two. It's been explained to me previously that this is due to trapped moisture in the element working its way to the ends.
I've also known elements fail open circuit. I believe I've seen short circuit but don't recall one

The reason I asked the question is that it's far more common for a customer to say "my RCD trips" if I turn the oven on than "my MCB trips". The early warning is commonly the RCD tripping.
That got me wondering if before the days of RCDs the leakage to earth could become noticeable to the touch.
 
Let's keep this discussion civil gents!
I've certainly known elements that are measuring respectable values when cold but will trip an RCD when energised after a minute or two. It's been explained to me previously that this is due to trapped moisture in the element working its way to the ends.
I've also known elements fail open circuit. I believe I've seen short circuit but don't recall one

The reason I asked the question is that it's far more common for a customer to say "my RCD trips" if I turn the oven on than "my MCB trips". The early warning is commonly the RCD tripping.
That got me wondering if before the days of RCDs the leakage to earth could become noticeable to the touch.

It's also caused by the element expanding and contracting, which then causes the filler to break down.
 
Let's keep this discussion civil gents!
I've certainly known elements that are measuring respectable values when cold but will trip an RCD when energised after a minute or two. It's been explained to me previously that this is due to trapped moisture in the element working its way to the ends.
I've also known elements fail open circuit. I believe I've seen short circuit but don't recall one

The reason I asked the question is that it's far more common for a customer to say "my RCD trips" if I turn the oven on than "my MCB trips". The early warning is commonly the RCD tripping.
That got me wondering if before the days of RCDs the leakage to earth could become noticeable to the touch.
I guess so, especially on a TT earthing system that is going to have a high earth loop impedance, but personally have never come across such an occurrence.
 
If you're quick enough with the megger after the RCD trips, you will see a rapidly increasing resistance. The resistance when measured cold is orders of magnitude higher than when the hot element trips the RCD. Presumably caused by the element moving by expansion/contraction.
On the type of elements we are discussing, the live and neutral terminals have a foot or so of element between them, so L - N shorts aren't normally possible.
I was around long before RCDs, and it wasn't at all unusual to see holes blown in the outer sheath of these elements, or even severed completely.
 

Reply to Oven Replacement - RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
933
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
D
Hi, I've searched these forums and have found quite a bit of good information, but not specifically to my query. My house is about 9 years old...
Replies
2
Views
2K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock