Beeg

-
DIY
Reaction score
16
Hi all,

Just after a bit of knowledge to satisfy my own curiosity - hope this is allowed within forum rules 🙂

I’ve just had a new kitchen installed and the electrician came today to connect two single ovens. They are each connected to their own MCB on different sides of the CU.
One of the ovens works fine, however one trips both RCDs when turning it on.

Having done a bit of Googling, it seems this can sometimes be caused by one of the neutrals being connected to the wrong busbar.
I understand why this would cause both RCDs to trip when the oven is turned on - one RCD would have x amps on the live coil and x+y amps on the neutral. The other RCD would have x amps on the live and x-y on the neutral, hence both RCDs are imbalanced.

What I’m struggling to understand is why the RCD on one half of the board can’t be reset without the other one first being reset.

Like I said, electrician is coming back in the morning so I’m not looking to fix anything myself, just curious.

Many thanks in advance
 
TL;DR
New oven trips both RCDs on CU - why do I have to reset one RCD before the other one will reset?

Reply to Oven tripping both RCDs in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
837
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock