Hello, anyone know why an overhead crane would cut out. It only cuts out when it gets to a certain point in the building. I have IR,continuity test on from control buttons to main panel. Tested windings of the motor all ok. Checked the busbar channel to ensure connectors have not worn down. 7 contactors, 4 were replaced around 2015 i am led to believe, 3 bigger contactors are quite old. Couldnt tell you how old lol. None of the breakers trip and the controls pull in the contactors but nothing happens. No drawings to go by as the manual is from late 70's.
 
If it is a track and brush for connecting the moving parts, I would look for damage or contamination.

recently been painted? A blob of paint on the conductive track would stop it dead.
 
If it is always in the same place that it fails, i would be looking very carefully at a bent, damaged, dirty or otherwise failed piece of conductive track.
 
Sounds some kind of contact fault. If you know where it's happening, it's a starting point. It's guesswork for us, though.
It looks like some careful live testing will need to be carried out ....so plenty care needed.
 
Is it just the travelling that cuts out or does the hook stop rising / falling.?
Is all power it via the Busbars or does it have trailing cables?
Does it stop in the same place with or without weight on it?
 
Is it just the travelling that cuts out or does the hook stop rising / falling.?
Is all power it via the Busbars or does it have trailing cables?
Does it stop in the same place with or without weight on it?
Everything cuts out, and yes has trailing cables. And always stops at the same place. Control buttons will pull in the contactors they control but nothing happens after that. I did do a IR,continuity etc on cables everything tested ok. And windings of the motor were good too. Cuts out with no weight on it.
 

Reply to Overhead crane in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Aside from every screwdriver in the universe, I wonder what the most creative mis-use of a tool you have encountered is. I'm sure this example can...
Replies
37
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock