Discuss Panel with Relay and SPD, Installation? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello and thanks for the interest. I have a little dilemma and was unable to get an answer anywhere.

I'm trying to fit a SPD and an over/under voltage protector to my existing "Main Switch" and "RCD" setup. my question: is the location of the SPD and surge protector correct? thanks
 

Attachments

  • meters3.jpg
    122.5 KB · Views: 34
Hello and thanks for the interest. I have a little dilemma and was unable to get an answer anywhere.

I'm trying to fit a SPD and an over/under voltage protector to my existing "Main Switch" and "RCD" setup. my question: is the location of the SPD and surge protector correct? thanks
What is the current rating rating of your surge protector? I have fitted Dehn SPD’s at a factory this year and to simplify matters the units are rated for 125A with big terminals so you can fit them without going through a Mcb first and Just off the main switch. If you use smaller cable to connect them then they come off a suitable rated mcb.
232EBF9E-9FA7-4C35-93CD-9B69FA8D68D0.jpeg
 
It looks like your main switch is in fact a double-pole MCB, is that correct?

Nothing wrong with doing that provided it is appropriate for the load, etc, but it would make selectivity with any down-stream MCB/RCBO very difficult to achieve (unless its instant trip point is above the PFC/PSSC of your supply at that point).

As already said above, many of the SPD are designed to be safe with supply fuses of up to 125A (or more) so you can normally get away with the supply's own fuse and use a simple DP switch. However, if your choice of SPD specifies a smaller breaker then you need to look at the design more carefully.
 
It looks like your main switch is in fact a double-pole MCB, is that correct?

Nothing wrong with doing that provided it is appropriate for the load, etc, but it would make selectivity with any down-stream MCB/RCBO very difficult to achieve (unless its instant trip point is above the PFC/PSSC of your supply at that point).

As already said above, many of the SPD are designed to be safe with supply fuses of up to 125A (or more) so you can normally get away with the supply's own fuse and use a simple DP switch. However, if your choice of SPD specifies a smaller breaker then you need to look at the design more carefully.
thanks for the detailed explanation. yes the diagram is of a double pole mcb but as per the text its just a main switch (a manual on/off). the switch is rated as 40a and the spd is rated at up to 60a. the spd is the one below:
 

Attachments

  • 1pc-AC-SPD-1P-2P-3P-4P-20-40KA-30KA-60KA-385V-House-Lightning-Surge-Protector.jpg
    79 KB · Views: 16
That is 60kA peak surge current, almost certainly for a 8/20us waveform.

You need to look up the data sheet to see what the maximum over-current protection is, and check that is above the incoming supply fuse.
 

Reply to Panel with Relay and SPD, Installation? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
921
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello! I'm struggling to find an answer to this question online. I'm new here btw - I'm a DIYer with a physics degree Currently when my fridge...
Replies
19
Views
1K
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock