Discuss Parallel generator, earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hello, can anyone advise on bonding of extraneous conductive parts when supply is from a generator run parallel with distribution network?
There'll b a 200kva generator supplying spray booths that have a gas supply to them.
The metal pipes aren't underground but connect to tanks outside sitting on concrete pads, could be bringing an earth into building so may need Bonding.
If they do can I run suitable bonding conductor back to generator MET independent of mains earth?
 
Looks like they will need Main bonding,sized appropriately,all main bonding back to the generator Earth terminal.
You may also have a main earth terminal too,these can be linked.
 
Presumably you are already in contact with the DNO about this if you are connecting a generator in parallel with their network.
This does raise the question of why you are doing this though?
If its just for the spray booth why not run that from the generator independant of the DNO supply?
 
Hi, should have said the existing supply is not fit to take the added load, cheaper to buy generator than increase supply.
I plan to run 50mm2 to a suitable 3ph high load board, independent from mains supply.
Earth the centre point of the generator with a 5/8 rod to get Ra as low as possible and bond the gas which only serves the spray booths.
That's the plan but I can't find anything in regs to confirm this is ok.
I'm thinking as long as both supplies are kept separate there shouldn't be any problems, there won't be any danger of gas bond rising from earth potential if there's a sound connection at generator, which I obviously intend on doing.
Can anyone else advise specifically on any other possible dangers that this install could create, or is my planned install suitable?
 
Hi, should have said the existing supply is not fit to take the added load, cheaper to buy generator than increase supply.
I plan to run 50mm2 to a suitable 3ph high load board, independent from mains supply.
Earth the centre point of the generator with a 5/8 rod to get Ra as low as possible and bond the gas which only serves the spray booths.
That's the plan but I can't find anything in regs to confirm this is ok.
I'm thinking as long as both supplies are kept separate there shouldn't be any problems, there won't be any danger of gas bond rising from earth potential if there's a sound connection at generator, which I obviously intend on doing.
Can anyone else advise specifically on any other possible dangers that this install could create, or is my planned install suitable?

You will need to be careful regarding notices on main isolator from grid supply.
warning that there is a second supply to the building, idealy with a diagram pointing to where this is isolated. (the fire brigade and other emergency services may have to isolate this when nobody is available to direct them)

my understanding is that this is no longer a generator running in parallel with the grid but seperatley to supply equipment that is not grid powered?

there are lots of regulations about grid tied generation, regarding synchronisation and disconnection etc. but it seems this is not the intention.
this document should help.
 
Yeah bit of confusion by saying the gen and supply are in parallel, my bad.
Good point about labeling, will make it clear there's a generator supplying some of the load.
Can't see anything specific about bonding in the document and there's nothing in regs, can I just size it based on neutral, same as tncs?
 
Hi sorry for delay in reply been busy.

From previous posts and my own research I think the install will be ok set up as a tns, with gas bonded back to generator MET.

My main concern was there could be a danger of bonding the gas to the generator creating a shock path from any other exposed or extraneous parts on the tncs earthing, provided by supply company. Basically any neutral currents in the supply feed part of the building could find there way to earth via generator earth, if someone was incontact with metal work from both supplies.

As the gas is only supplying the spray booths and there are no other extraneous parts entering that area it should be safe. Also the spray booth area only has circuits from generator supply feeding into it so again I see no danger of contact from both supplies.
Maybe worth telling client that no extension leads should be run into spray booths for other equipment, it will have to remain isolated from the rest of building supply.

If anyone else has any more to add please let me know, thanks.
 

Reply to Parallel generator, earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K
Just a bit of a muse at the moment, work won't happen for a while, though I do already have the ducting. We have (what's left of - it was rotten...
Replies
0
Views
1K
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top