Octopus

All,

Been to see a job today and its a kitchen refit, - moving sockets mainly, in a well established "park" home near me.

The homes are of "caravan" type construction, but are effectively permenant as they are plumbed into the sewers etc. Each one has an electrical supply from a "central point" so they do not have individual meters by each unit nor could I locate any form of supply "fuse". The residents pay the park for their leccy!

This is a picture of the RCD which is before the fuseboard..



Park Home RCD.jpg

The Ze was 1.8 ohms which would "suggest" a TT but I couldn't see a rod anywhere!. The Zs on the ring was a respectible 2.26 ohms.

There wasn't any bonding to the water so that needs to be sorted and the gas is from a LPG bottle.

So the question is should I put a rod or two in or leave the earth connection as is?

NB: I tried to meet with the site maintenance manager and he was off site today and yes I know the supply cable is small!

Thanks
 
i'm thinking that it's a TN system but your readings are high due to the length and small csa of the supply cable. what i have found with these park homes is that 2 or 3 homes will be fed from a pole with an isolator for each and at the pole it's TNC-S. the ones i've worked on have has meters at the poles as well.
 
i'm thinking that it's a TN system but your readings are high due to the length and small csa of the supply cable. what i have found with these park homes is that 2 or 3 homes will be fed from a pole with an isolator for each and at the pole it's TNC-S. the ones i've worked on have has meters at the poles as well.

Thanks. Just wish I could have seen the Manager and taken a look at the "supply" which is locked away!
 

Reply to "Park Home" question in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hay guys and gals, doing my first park home CU change. I cannot find a copy of an installation cert for a portable dwelling can anyone point me in...
Replies
9
Views
1K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
556
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
725
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock