Hi,This might sound like a stupid request but how with a standard pat tester do you test a cooker when you can not plug the 6mm into the s/o of pat tester or do you just croc clips on to cable then test.Thx
Discuss Pat test on cooker in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
I just pat tested a cooker, it was a flex with plug for the ignitor but did'nt actually test the whole cookerThx for that,is that a FAT test then, its just that i was working at a house and they are going to rent it out and asked for the cooker to be tested.
Its not a portable appliance , but when carrying out the fixed wire test it worth testing it in the same manner ( continuity , IR , Earth test ), especially if there is age to the cooker
-------------------------------------------------------------------
you could make up your own test lead to pat tester to do this
this is something i did with my pat tester so i could do the earth bond test at 25Amp as most continuity testers only do the earth screen continuity test @ approx 200mA
you could make up your own test lead to pat tester to do this
this is something i did with my pat tester so i could do the earth bond test at 25Amp as most continuity testers only do the earth screen continuity test @ approx 200mA
So how did you do this ?
Thanks for that - trouble is invariably you're at a client that says "Oooh Noo! We don't want the power off - that'll upset all sorts of stuff."
So an "In Situ" test is the best you can provide - at least 100mA earth bond test is better than not at all, and visuals of course (in this case) are the main criteria for this equipment. (Seaward recommend from their COP Rev3 seminars.)
It may be good practice to try a continuity test or insulaltion tests on these items but Im curious to know whether the cooker/heater comes under the unbrella of portable aplliance testing?
I mean, some where down the line they should be checked, these pieces of current using equipment, defined as appliances.
I have a landlord mate who is questioning this. He doesn't leave items with plugs on in the flats he rents out but there may be cookers and heaters, hard wired into flex outlets and is unsure whether these pieces of equipment need the Pat test. Secondly, these are in domestic properties, so Im unsure if the PAT testing is a lawful requirement as they are not at work.
It all boils down to insurance companies who may or may not insure your house based on what is or isnt required with regards to fixed current using equipment under a portable applaince test.
There is NO STATUTORY LEGAL requirement for PAT in ANY environment.
Anyone who says there is is an idiot and does not understand the statue law in this area.
End of.
A cooker should still be tested. The idea that it's called portable appliance testing and a cooker is not intended to be moved during use is just a lazy play on words; swapping a plugtop for a FCU doesn't negate the need for testing.