Discuss Pat testing: Class 2 printers and laptop power packs???? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

J

jameswalters33

Hi I'm a little confused, sure this has been asked on here before but I'm pretty new to forums

Could you tell me if the following about PAT testing is correct

Class I printer, plug in printer IEC Lead into pat tester test as a lead Earth, Insulation and Polarity. Plug lead back into printer find earth on metal part of printer and test as Earth and Insulation res?

Class II printer I'm a little confused PAT TEST mickey mouse lead earth, insulation and polarity, what about the power pack and the printer?

Also do mobile phone Class II chargers need to be pat tested or will a visual do?

Laptop chargers do they need PAT Testing I know you need to test the lead but will a visual do for the power pack?

Also is a laptop power pack charger class I or II they never say isit by the lead it takes as I've seen class I and class II leads going into these laptop power packs

Many Thanks
 
Class 1 Printer ( the big ones like Xerox/seiko/mitsubishi) test the IEC Lead @ 25A then check the fuse size, then use one of the Rivets or screws on the back for the probe test for earth bonding......don't use the metalwork on the Network card where the Cat 5 cable goes into it from the office network (the Plastic RJ11 connector with network cable) as this will fry the network card...use another bit of metalwork on the back....
Always unplug the network cables from the printer as they will cause incorrect earth readings as the outer thin metal sheath (screen) in the cable will connect the printer earth/case earth directly to the PC( The PC power Supply earth, Case that is connected to this, as well as the mainboard/motherboard) that it is connected to....

Making sure that the network connector cables are removed during testing will also save you from damaging any Laptop/Netbook that is connected, the network card in those is 99%of the time part of the mainboard (or as Laptop techies call it the "Logic Board") and is pricey to repair if you don't do repairs yourself...


Class 2 printers (Plastic Desktop ones like Epson or KODAK ones) take out the figure 8 lead and insulation test it with an adapter, then check that the fuse in the plug is the correct size(such as 5A, or 3A and not a 10A or 13A fuse) give it a quick once over to make sure no broken open plastic around the mains parts as a visual.....

Mobile phone Adaptors/chargers are a visual check only as they are SELV straight from the plug pins into an isolated transformer then a rectifier and regulator inside, encompassing some switched mode power supply circuitry...output is low voltage so its just a visual check...

Laptop chargers: check that the power pack box/case is not broken or split open, then check that the low voltage output lead that goes into the laptop is not split open, so as to avoid fraying of the outer part of the conductor ( these are mostly small co-axial flex with the inner core as +Ve and the outer stranded sheath/conductor as GND -Ve) from causing overheating, as if it is hanging on by a few strands it can heat up during use when it will be carrying a reasonable bit of current (usually anything up to 15A DC) and melt/start a fire......if the charger case and the outgoing fixed/built in lead are ok, then check the IEC lead (or cloverleaf lead-adapters to fit PAT machines are on ebay for about £3) using a 25A IEC lead test on the PAT tester, check that the Fuse is the right one (almost always a 10Amp one, sometimes a 5A on Netbook chargers, Never Ever a 13A) then that's you done apart from the sticker and paperwork..


Laptop chargers are almost always Class 1 (3 pin input plug) Netbook (miniature laptops) are 50% figure 8 leads(Class2) and 50% Class 1 (on an IEC 3 pin supply lead) depending on the manufacturer...
 
Class 1 Printer ( the big ones like Xerox/seiko/mitsubishi) test the IEC Lead @ 25A then check the fuse size, then use one of the Rivets or screws on the back for the probe test for earth bonding......don't use the metalwork on the Network card where the Cat 5 cable goes into it from the office network (the Plastic RJ11 connector with network cable) as this will fry the network card...use another bit of metalwork on the back....
Always unplug the network cables from the printer as they will cause incorrect earth readings as the outer thin metal sheath (screen) in the cable will connect the printer earth/case earth directly to the PC( The PC power Supply earth, Case that is connected to this, as well as the mainboard/motherboard) that it is connected to....

Making sure that the network connector cables are removed during testing will also save you from damaging any Laptop/Netbook that is connected, the network card in those is 99%of the time part of the mainboard (or as Laptop techies call it the "Logic Board") and is pricey to repair if you don't do repairs yourself...


Class 2 printers (Plastic Desktop ones like Epson or KODAK ones) take out the figure 8 lead and insulation test it with an adapter, then check that the fuse in the plug is the correct size(such as 5A, or 3A and not a 10A or 13A fuse) give it a quick once over to make sure no broken open plastic around the mains parts as a visual.....

Mobile phone Adaptors/chargers are a visual check only as they are SELV straight from the plug pins into an isolated transformer then a rectifier and regulator inside, encompassing some switched mode power supply circuitry...output is low voltage so its just a visual check...

Laptop chargers: check that the power pack box/case is not broken or split open, then check that the low voltage output lead that goes into the laptop is not split open, so as to avoid fraying of the outer part of the conductor ( these are mostly small co-axial flex with the inner core as +Ve and the outer stranded sheath/conductor as GND -Ve) from causing overheating, as if it is hanging on by a few strands it can heat up during use when it will be carrying a reasonable bit of current (usually anything up to 15A DC) and melt/start a fire......if the charger case and the outgoing fixed/built in lead are ok, then check the IEC lead (or cloverleaf lead-adapters to fit PAT machines are on ebay for about £3) using a 25A IEC lead test on the PAT tester, check that the Fuse is the right one (almost always a 10Amp one, sometimes a 5A on Netbook chargers, Never Ever a 13A) then that's you done apart from the sticker and paperwork..


Laptop chargers are almost always Class 1 (3 pin input plug) Netbook (miniature laptops) are 50% figure 8 leads(Class2) and 50% Class 1 (on an IEC 3 pin supply lead) depending on the manufacturer...

My pat tester IR tests between line/neutral joined together and earth,therefore IR testing a 2core lead would be pointless. Only IR test a class 2 printer using the auxillary IR probe onto any exposed metal....if the printer has no exposed metal visual only
 
you can get adapters for figure 8 2 core leads...as well as cloverleaf adapters and others for lighting rigs and stage equipment, industrial commando sockets etc...
 
Not enough information.

Depending on the type of premises, C2 equipment may require no combined inspection and testing (hotels, offices and shops) - read through your CoP.
 
or just stick a sticker on it as passed and charge £0.10 which everyone seems to be doing these days.

"my appliance isnt working and uve passed it recently" "....it must of broke / become dangerous since i was last their then because it tested out fine on the day, and my equipment is calibrated"
 
OK thanks for the advice thats pretty much what im doing with the class I printers

Class II just test the lead basically? but the printer also needs a visual so a sticker for each?

What about if you find a fig 8 lead going in to power pack then to the printer?
 
Not enough information.

Depending on the type of premises, C2 equipment may require no combined inspection and testing (hotels, offices and shops) - read through your CoP.

Is there not a proviso? May require no combined inspection and testing provided the formal visual inspection (which is recorded) is made? This point is made also on the HSE website.

Also, some powerpacks for laptops and printers do not have the double insulated box on them. (Only if an appliance has the double insulated box can it be considered as class 2). If so, the earth bond test is to be done. Added check, if the earth pin is metal, think about earth.
 
My pat tester IR tests between line/neutral joined together and earth...

As does every PAT tester

therefore IR testing a 2core lead would be pointless.

Quite right. A fact that seems to repeatedly escape many

you can get adapters for figure 8 2 core leads...as well as cloverleaf adapters and others for lighting rigs and stage equipment, industrial commando sockets etc...

Still pointless IR testing a 2-core mains lead.
 

Reply to Pat testing: Class 2 printers and laptop power packs???? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
518
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
714
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
My understanding is that a SMPS does not separate, like a SELV transformer, the secondary from the primary. Therefore presumably the equipment...
Replies
4
Views
849
I got dragged into a PAT testing argument....I don't miss this kind of thing! Cheap and horrible display stand lights. IEC plug. Class 2 symbol...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock