PAT Testing Method ?????

Discuss PAT Testing Method ????? in the UK Electrical Forum area at ElectriciansForums.net

D

Dizzy_Maskell

Guys just for your thoughts,

I was on a site recently and we encountered the local PAT guy, luckily we as a company don't do PAT so I have limited knowledge on the subject.

He was using an extension lead and testing about 10-15 items in one go and then stickering them all up after testing all the items in one hit.

We asked him out of curiosity if you can do this as we where not sure and he advised it is the equivalent of a global test when doing IR testing. He told us that if all 15 etc pass in one go then individually they must pass so of course it is ok.

Just looking for people's opinions on this as I have limited PAT knowledge has anyone else seen this done ????
 
Actually I think the justification could only be for Class I - as the cpc connection is there and therefore you will get the insulation resistances in parallel. For Class II it is no good as you would need to test between live conductors and exposed metalwork etc. which clearly would require you to probe each asset.

But as said, even with Class I, then it leaves the problem of needing to conduct an earth bond on each asset - so is there any real benefit? I suspect not.

Another problem is that you would have to verify that the fuses were all intact for the insulation resistance test to be meaningful.

Not sure if you are a little confused there.
Class 1 are appliances with earthed and exposed metal work.
Class 2 is double insulated.

Therefore with class 1 you have to do a earth bond test on each appliance.
With a basic class 2 then its on IR.
 
I doubt this guy has even got a PA-Tester hows he go about flash testing class II approx mine is 1.5-3kv dependent on whether the item has been repaired or not in its past.

Hows will he achieve a flash test me wonders i assume he hasn't got a proper PA-Tester as most now do all the checks in sequence and this would not see you global testing.
 
completely gob smacked

Guys,

We did an EICR on an entire site a few weeks ago the site consists of numerous out buildings, sheds, maintenance shops etc. The site is entirely covered in Tarmac and all cables to these various buildings fed from a main sub are SWA cables using the armouring as the earth

The issue is that all out buildings etc the earth loop impedance is too high.

The earth loop in the Sub is fine but due to length of run etc the earth loop at all the boards is too high.

We have advised the site about this and explained they need to run separate earth to each out building with the cable.

They have come back to us today after their electrician has said he plans to run an earth ring around the perimeter of the site tapping in to each building as required instead of digging up the Tarmac to each building,

How he plans to do this we are yet to hear but I think I can hear a yeeeee haaaaaaa in the horizon
 
I doubt this guy has even got a PA-Tester hows he go about flash testing class II approx mine is 1.5-3kv dependent on whether the item has been repaired or not in its past.

Hows will he achieve a flash test me wonders i assume he hasn't got a proper PA-Tester as most now do all the checks in sequence and this would not see you global testing.

Ya know I have never flash tested a single appliance LOL
Most modern testers dont even have the capability I dont think, Our old robin can do it but never been needed.
 
guys,

we did an eicr on an entire site a few weeks ago the site consists of numerous out buildings, sheds, maintenance shops etc. The site is entirely covered in tarmac and all cables to these various buildings fed from a main sub are swa cables using the armouring as the earth

the issue is that all out buildings etc the earth loop impedance is too high.

The earth loop in the sub is fine but due to length of run etc the earth loop at all the boards is too high.

We have advised the site about this and explained they need to run separate earth to each out building with the cable.

They have come back to us today after their electrician has said he plans to run an earth ring around the perimeter of the site tapping in to each building as required instead of digging up the tarmac to each building,

how he plans to do this we are yet to hear but i think i can hear a yeeeee haaaaaaa in the horizon

sorry meant to be new thread
 
Ya know I have never flash tested a single appliance LOL
Most modern testers dont even have the capability I dont think, Our old robin can do it but never been needed.

If an item is double insulated the integrity of the insulation has to be clarified and this can only be done with the flash test as basic insulation testers dont have a high enough voltage output or ability to sustain the voltage to do a full flash test... i take it you never tested a class II in your life then :smilielol5:eek:r you avoid the whole senerio altogether ... we used to have a manual PA-Tester but i got a Martindale micro-pat+ just press a few buttons and let it cycle only pressing advance when the set-up needs changing.
 
If an item is double insulated the integrity of the insulation has to be clarified and this can only be done with the flash test as basic insulation testers dont have a high enough voltage output or ability to sustain the voltage to do a full flash test... i take it you never tested a class II in your life then :smilielol5:eek:r you avoid the whole senerio altogether ... we used to have a manual PA-Tester but i got a Martindale micro-pat+ just press a few buttons and let it cycle only pressing advance when the set-up needs changing.

Tested more than my fair share sadly :(

However regarding flash testing when I did the course many moons ago we were told to only carry out flash testing if the appliance had been repaired or was suspected of having the insulation breaking down.
Reason being that flash testing can damage the appliance and that they are flash tested by the manufacturer.

So yeah ive never carried one out.
I have sold my tester now but it did not have the ability to do a flash test.
 
Was told similar but as i work in factories everything i touch has been repaired and hand grinders filling up with metal dust means i get alot of fails so for me and my circumstances its a regular crucial test..... had a guy get a shock off a double insulated drill 230v ... the circuit was rcd covered and tested working fine but it hadn't tripped so obviously leakage not high enough but was down to fine metal dust from the workshop settling on the com' brush holder and tracking to the metal case.... it failed the flash test but passed a normal insulation test to same point..... high pressure dried compress air line did the job ..... yep your correct about the flash test use but in a factory it would be used a bit on the bench tools.


Yes i know it should ideally be 110v gear but you test what they got and advise accordingly it up to them to listen or not but least i fitted rcd protection on all 230v outlets.
 
Last edited:
Was told similar but as i work in factories everything i touch has been repaired and hand grinders filling up with metal dust means i get alot of fails so for me and my circumstances its a regular crucial test..... had a guy get a shock off a double insulated drill 230v ... the circuit was rcd covered and tested working fine but it hadn't tripped so obviously leakage not high enough but was down to fine metal dust from the workshop settling on the com' brush holder and tracking to the metal case.... it failed the flash test but passed a normal insulation test to same point..... high pressure dried compress air line did the job ..... yep your correct about the flash test use but in a factory it would be used a bit on the bench tools.


Yes i know it should ideally be 110v gear but you test what they got and advise accordingly it up to them to listen or not but least i fitted rcd protection on all 230v outlets.

Ahh thats interesting.
Cant say I have ever come across that sort of situation.
Our factories pretty clean and most of the hand tools are battery powered but I shall keep that in mind for the future :)
 
Lots of welding and grinding etc and lack of extraction system in my factories means conductive dust and soap in the coolants burning off then it layers up inside the DC motors .... regular filter changes on control cabs and motors require steam cleaning throughout and baking dry at least every few years ... be nice to be just PA-Testing a kettle in kitchen if i had the choice but like everyone i hate doing it with a passion!
 
I doubt this guy has even got a PA-Tester hows he go about flash testing class II approx mine is 1.5-3kv dependent on whether the item has been repaired or not in its past.

Hows will he achieve a flash test me wonders i assume he hasn't got a proper PA-Tester as most now do all the checks in sequence and this would not see you global testing.

When I come across an item of equipment that I'm unfamiliar with I just pull my trousers down. If it doesn't move then its been Flash tested.

No need for 'Claire' .......
 
Class 2 kit can need a probe applied sometimes if it has exposed metalwork, not necessarily a flash test though.

On the fluke 6500 we use, and according to the manual for it the probe should be applied to teh exposed metal parts of class 2 kit whilst the insulation test is being carried out. Its the same for a substitute leakage test and a touch current test.
 
Class 2 kit can need a probe applied sometimes if it has exposed metalwork, not necessarily a flash test though.

On the fluke 6500 we use, and according to the manual for it the probe should be applied to teh exposed metal parts of class 2 kit whilst the insulation test is being carried out. Its the same for a substitute leakage test and a touch current test.

Yes you are correct but lets clear this up to exactly what i mean ... class I equipment is flash tested to 1.5Kv and class II is at 3kv by the manufacturer now like in my senerio a item is repaired or stripped and serviced then the item should be subject to the same original testing that was required by the manufacturers.

PA-Testers who are rarely in my set-up (heavy industry) can buy a PA-Tester that doesn't afford this option but if you are doing equipment that is serviced and repaired on site you need to maintain it has full integrity as expected from a manufactured new condition thus flash testing required. If you are testing repaired equipment then you should have a meter capable of a 1.5-3kv flash test!

Flash testing for me is essential as it indicates metal dust contaminants building up ...ideal for pre-empting a failure or worse a hazard.

Driving a mini around Silverstone will get you from A to B but if you need to drive the course as it was designed you are going to need to spend a little more money on a car that can achieve this!
 
Last edited:
Not sure if you are a little confused there.
Class 1 are appliances with earthed and exposed metal work.
Class 2 is double insulated.

Therefore with class 1 you have to do a earth bond test on each appliance.
With a basic class 2 then its on IR.

No, not confused. A Class II appliance may not be insulation-enclosed and as such may have exposed metalwork and you need to verify that there is in fact no path between this and live parts. This can only be achieved by applying the probe.

A PAT tester tests between live conductors connected together and the cpc pin. With a Class II appliance - which has no cpc - then the insulation test will not actually test anything unless a probe is applied as there is no potential difference between the live conductors. Without the probe you are simply proving that the air between the asset and the tester is not conductive!
 
I have never yet had to test equipment in that area.

Most of the kit I have to test is reasonably specialised to another sector, the entertainment industry, so has its own little nuances to be considered. A lot of it gets tested with my MFT in the same manner as an installation test and a very thorough visual inspection.
I'd love to watch one of those PAT monkeys try and test one of these

distro.jpg
 
I have never yet had to test equipment in that area.

Most of the kit I have to test is reasonably specialised to another sector, the entertainment industry, so has its own little nuances to be considered. A lot of it gets tested with my MFT in the same manner as an installation test and a very thorough visual inspection.
I'd love to watch one of those PAT monkeys try and test one of these
Well each segment of the industry to there own i could do with one of them linked and phase shorted to my meter to test the multitude of plug top styles lol ;)
 
You certainly end up with a big selection of test adaptors made up for doing them. The other side of the box is normally a forest of MCB's RCD's and variable RCD's, you can easily get bored of RCD testing with one of them!
 
You have to wonder who comes up with idea for these new testing methods what next do a global PAT test at the consumer unit or DB given the size of some of these office blocks you could be testing ???? appliances in one hit makes these few hundred a day lads look like beginners
 
No, not confused. A Class II appliance may not be insulation-enclosed and as such may have exposed metalwork and you need to verify that there is in fact no path between this and live parts. This can only be achieved by applying the probe.

A PAT tester tests between live conductors connected together and the cpc pin. With a Class II appliance - which has no cpc - then the insulation test will not actually test anything unless a probe is applied as there is no potential difference between the live conductors. Without the probe you are simply proving that the air between the asset and the tester is not conductive!

One thing this thread has highlighted is how many pat testers just plug a class 11 appliance into the tester...press IR test and assume it's actually tested something!
I had a row on here once with a guy who insisted all insulated moulded phone chargers could and should be IR tested,thats the standard of understanding of yer 'competant person'
 

Reply to PAT Testing Method ????? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock