Discuss Peak output exceeding quoted panel output? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

M

MattyNeth

Hi - I have a 2.99kW solar array, and the top output I have had had previously been yesterday's 2800w at one point at lunchtime which I was more than pleased with as I was under the impression the maximum could be 2999w? Today on 3 occasions output was over 3000w (peak was 3080w). Have I got the wrong end of the stick here?!
 
On the MSE forums a member has posted that her Sanyo HIT 3.84kWp and 4.4 Eltek HE-t inverter has peaked at 4.458kW and held for 15 minutes which confuses me!
 
The stated output is under standard test conditions. In certain combinations of sunlight and temperature, it is possible for panels to exceed their nominal rating.

In addition, it is possible for a 3.6kW "G83/DNO-approved" inverter to exceed 3.6kW output if the local grid voltage is higher than 230V.

I posted the following a few days ago, where my KV-250 panels were managing as much as 265W, and my 3.6kW inverter was managing to put 3.7kW into the grid.

Link -> http://www.electriciansforums.net/photovoltaic-solar-panels-green-energy-forum/54687-full-power.html

.
 
Oh, and the inverter's on-screen readings were confirmed by me using a stopwatch to time the rate of flashing on the generation meter next to the fusebox; the rate of flash was about 20 flashes per 19 seconds (meter does 10 flashes per 0.01kWh) and it repeated this phenomenon today just before lunchtime.
 
Panels also have a tolerance of eg +/- 3% this varies from panel to panel!

I would expect that all panels in the array would need to be operating at that higher level, otherwise the array woudl run at the ability of the weakest link.


The KV's in my array are stated to be 0 to +5 W tolerance, and are sold as a variety of models, simply sorted by their "flash" test at the factory. For example, there's KV240 (240-244.9W), KV245 (245-249.9W), KV250 (250-254.9W) panels which are identical, other than some had a higher flash test output than others and have been sold at a better price.

But the output, as mentioned earlier, is quoted under standard conditions of light and temperature.

A few days ago, when my KV250's approached 265W, but it was a very sunny, very clear, cool and breezy day. The sun was probably as strong as standard test conditions, but it was cooler and breezier, which probably helped boost the output of the panels compared to a hot day.
 
Isn't the capacity the safe continuous output? i.e. the safe continous capacity in the O.P would be 2.99kw but that dosen;t mean it cannot exceed it , just not contiunously?
 

Reply to Peak output exceeding quoted panel output? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I thought I had an understanding of how to size an inverter but I think I have become slightly confused after taking to some proposed installers...
Replies
3
Views
2K
TLDR - I have a system that is supposed to have optimisers fitted, but I am not sure they have been fitted. The detail: Back in March I had a...
Replies
11
Views
3K
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
775
Sorry if it's in the wrong spot, feel free to move. The specific setup: 12v Bilge Pump wired to a 24v solar panel with a resistor (I think). The...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock