Search for tools and product advice,

Discuss Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
27
Hi guys I’m not carrying out a periodic but have seen in a house a lighting circuit with no CPC which I know was acceptable at the time of install but the circuit contains class one equipment. The circuit is RCD protected but would this be classed as a C2 as the RCD can’t be relied on for fault protection due to there being no earth path?
Thanks guys
 
Have a look at best practise guide 4 (free download) as it mentions this scenario.
Opinions vary about how to code this. A forum search will give you lots of reading material!
 
Class 2 fittings have no connection for a cpc, therefore the presence of a cpc at the fitting is irrelevant, as it will not be connected to anything accessible, or any part of the fitting at all. Therefore it is not "potentially dangerous - urgent remedial action required" - the definition of C2.
It does not comply with current regulations, however, so C3 it is.
 
I think the argument here is, that if there is no cpc, but there’s metal fittings that need a cpc, then changing the fittings is not the answer…. C2, potentially dangerous. Rewire the circuit.
Changing the fittings is a bodge solution

if there is no cpc, and the fittings are already class II, then that’s C3- improvement.
 
EICR is like a car MOT test. It is a snapshot of here and now.
If there are class 1 fittings present, then on that EICR, it is coded C2. If the fittings are then replaced with class 2, and a new EICR is performed, then it's C3. What there may have been as part of the installation yesterday is of no concern to someone carrying out an EICR today.
 
Thank you guys your comments have been very helpful! Just one more what are are duties and if we are carrying out an EICR and we spot a C2, I know for a C1 we’d make safe as there is a danger present but a C2 it’s only present if a fault occurs. Just trying to get my head clear for my 2391-52?
 
Thank you guys your comments have been very helpful! Just one more what are are duties and if we are carrying out an EICR and we spot a C2, I know for a C1 we’d make safe as there is a danger present but a C2 it’s only present if a fault occurs. Just trying to get my head clear for my 2391-52?
I'm not trying to be funny but out duty is to inspect and test according to the agreement with the client. If we find C1's we need to exercise judgement about whether to isolate or negotiate an instant fix (sometimes the rest of the inspection needs to be delayed to accommodate this). If we find C2's then by definition they are still one fault away from instant danger and the person receiving report has the responsibility to arrange the necessary work.
Of course we can quote for that work, and sometimes clients prefer to say "fix as you go" within reasonable constraints.
Does that help, or confuse further?!
All the best for your exam.
 

Reply to Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
724
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock