Discuss Phases in dado trunking. in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
7
Hi all and thanks in advance for any replies.
I was wondering if whether when having more than one phase inside a dado trunking are you required to mark up the trunking with a 400v marker/label like you would at a multi gang light switch??
Cheers
 
Hi all and thanks in advance for any replies.
I was wondering if whether when having more than one phase inside a dado trunking are you required to mark up the trunking with a 400v marker/label like you would at a multi gang light switch??
Cheers
No requirement.
According to bs 7671 a warning label is only required when the line to earth voltage exceeds 230 volts ac. You would only have 400volts between phases.
I still however label a 3phase db with a 400v sticker/warning notice just the way I was taught and I think it's good practice
 
Last edited:
Hi all and thanks in advance for any replies.
I was wondering if whether when having more than one phase inside a dado trunking are you required to mark up the trunking with a 400v marker/label like you would at a multi gang light switch??
Cheers
I don't know if it's a requirement (ignore that cheers lee:D) but I certainly would, not a big sticker but maybe the smaller etched ones placed on the lid, just in case someone who isn't competent decides to have go at chucking a couple of extra sockets in.
 

Reply to Phases in dado trunking. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
756
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
338
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
407

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock