Discuss Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all, 2nd year apprentice.

I'm looking to take a supply out to my garage, which is detached, from the DB at the front of the house (2 bed terraced, built 1978~)

The length of run is about 30m (having to go through either loft or under floorboards).

Intend to have a 20A radial and a 6A lighting circuit so am I right in thinking I'd allow 66% diversity for lighting and 50% for the power circuit as it's over 10A? So 13.96A total demand?

Thanks 😊
 
in practical terms, a garage supply will always (well nearly always) want a 32A supply as a minimum.
In the winter, there will inevitably be a 3Kw fan heater and the starting current of the angle grinder, chop saw, welder, hot tub, lawn mower, or any other of the common things plugged into a garage.
 
in practical terms, a garage supply will always (well nearly always) want a 32A supply as a minimum.
In the winter, there will inevitably be a 3Kw fan heater and the starting current of the angle grinder, chop saw, welder, hot tub, lawn mower, or any other of the common things plugged into a garage.
For my needs it will just be for a fridge/freezer, tumble dryer and use of garden/home equipment to hoover my car and trimming hedges.

But yeah if and when I move on one day someone else may want the extra capacity for more. Let's say I took 40A out there, what would I do for a mains switch in the dB?
 
ha, ha.

fridge/freezer 2A continuous 10A start
tumble drier 9A continuous 13A start
Vac. cleaner 8A continuous 13A start.

I rest my case.
 
For my needs it will just be for a fridge/freezer, tumble dryer and use of garden/home equipment to hoover my car and trimming hedges.

But yeah if and when I move on one day someone else may want the extra capacity for more. Let's say I took 40A out there, what would I do for a mains switch in the dB?
What do you mean mains switch in db? You could just add a 40a mcb to your existing db if using swa and fit a small board in the garage, with rcd protection of course
 
What do you mean mains switch in db? You could just add a 40a mcb to your existing db if using swa and fit a small board in the garage, with rcd protection of course
Well I was going to use RCBOs due to the built in RCD protection at the main DB in house. Then at the garage sub main dB have a main switch to isolate the two breakers on that board.

Hope that makes sense haha
 
If you fall out with the miss’s and are crashing in the shed one night and your RCBO trips right in the middle of a good movie, you will have to trail back to the house in the dark to reset the RCBO. Better design required, ideally with your RCBO at the shed end.
 
Detached garage, so buried cable between? Need SWA.
SWA does not need rcd protection.
The circuits from the board in the garage will.

What is in the house board at the moment? Mcb? Rcd? Photo please.


Are you working with a company? What do your colleagues suggest?
 
You will always end up needing more than you planned for!

There are a few ways to approach the design and you should go with the largest of:
  • What loads do I expect to use?
  • What is my basic cable choice capable of?
  • What cable size can I afford if looking to future usage?
You are unlikely to select less than 2.5mm SWA so buried it should be fine with a 32A MCB, but what is your route and hence the "methods" involved? They might lower the CCC if it runs through insulated regions.

Will you meed voltage drop with this choice?

Do you have extraneous conductive parts in the garage? If so do you need to size for PME bonding requirements?

What is your supply Ze and so can you meet sub-main disconnection time with the cable length and your chosen protection?
 
Well I was going to use RCBOs due to the built in RCD protection at the main DB in house. Then at the garage sub main dB have a main switch to isolate the two breakers on that board.

Hope that makes sense haha
Your swa cable does not need rcd protection. Personally I would have it on an mcb and either small board with rcbcos or rcd in garage.
 
40 amp mcb, 10mm 3 core swa, garage Cu, would cover most garage supplies and allow for future upgrades.

If there really is the likelihood of say an Ev point or hot tub, then I would use an SP+N fused connection unit.

But like already said, more information is needed.
 
Last edited:
Cheers for the replies, much appreciated.

So the db is in the porch on the ground floor (highlighted red) and the first floor pic with red lines is my proposed route going under the floor boards or up into the loft.
 

Attachments

  • Screenshot_20230620_184955_Rightmove.jpg
    141.8 KB · Views: 15
  • Screenshot_20230620_184949_Rightmove.jpg
    128.7 KB · Views: 20
I will run the T&E down the wall.either from the loft or from under the floor on the first floor (half way down) into a joint box with the swa which will go to the garage
 

Attachments

  • 20230620_184650.jpg
    194.1 KB · Views: 19
The right hand side of your board with the lighting MCBs isn't RCD protected and the blank will be a spare way- so subject to a decent Ze you could simply fit an additional matching MCB for the new SWA, but it will have to be glanded properly, possibly into a small metal enclosure to ensure the armour is earthed. EDIT= Ah I've just seen your post stating T&E for the first part of the run, so the SWA can be glanded into a weatherproof enclosure with an earthing nut and lead to the CPCs.
 
Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it
 
Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it
Well I was thinking twin and earth (e.g. 6mm) would be cheaper and easier to run under floor boards etc.

Tbf I could use that blank space for a 40A MCB to supply the garage couldn't I 👀
 

Reply to Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
902
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
732
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
559
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K
This is a question with probably so many answers and solutions, but I wondered how people would do it. I have a clients house which already has...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock