Good old amendment 3 and the demise of all that's plastic, we have seen many discussions on the good old plastic consumer units, so now for those EICR's where plastic has and will be around for quite some time, SO !!
We all seem to have slightly differing views on this, but here goes.
C2 if there are signs of thermal damage ( I think we would all agree with that one)
C3 dependant on certain locations ie only route of escape or under a staircase.
Other than that no code ?? with just an observation ?? Or no code with no comment at all ??
Throwing a spanner into the works, I code 3 ALL plastic consumer units, but why !!
Of course I could just say its my signature and my decision, plus a C3 is not failing the install, but there's another reason.
Before saying, I would be interested to see what your thoughts are, as I think this could prove quite interesting.
 
I tend to make a note of the type and layout of the consumer unit in the general comments box. i.e split load Hager plastic CU.

I only code when I feel it is warranted, not as a default.
 
C3 by default is understandable (afterall the code is defined as Improvement Recommended); if nothing else it's arse-covering and doesn't fail the EICR; Much like any other nonconformities to current 18th edition; C3 so it's on record in more than just a 'passing comment' and is inkeeping with the purpose of the C3 code - obviously go further attaching relevant regs from 7681, EAWR and that like where appropriate to further explain your engineering judgement.

I find it interesting that we focus on CUs being non-plastic and yet permit things like REC2 Isolators (with or without SPD) and Thier assemblies to be plastic, along with adaptable boxes, for that main being plastic - I believe 5839 makes an stipulation that any junction boxes et all are to be metalic to ensure system integrity bit would have to find out the relevant clauses to confirm.
 
I wonder how long it will be before this goes even further and we have metal MCB's, RCD's, RCBO's and main switch's, even to the extent of T&E being metal sheathed, or maybe back to metal conduit becoming compulsory.
 
I wonder how long it will be before this goes even further and we have metal MCB's, RCD's, RCBO's and main switch's, even to the extent of T&E being metal sheathed, or maybe back to metal conduit becoming compulsory.
What about lead sheathed cables ? Mad idea, but it might work...
 
Thanks for the replies, as said we all have our reasons for coding these things or not coding as we feel fit.
For what its worth, I like most have seen these reports gain page after page as times gone on. In particular the Inspection schedule has become very comprehensive.
So looking at section 4 and in particular 4.4
I feel where plastic CUs are concerned, we have little choice but to C3 as an absolute minimum. If Regulation 421.1.201 isn't met. ie condition of enclosure in terms of fire rating. Then I will be covering my proverbial. Sometimes I see these schedules as trick question scenarios.
So default Code 3 thankyou IMHO.
As said cover your arse, its your signature.
 
So looking at section 4 and in particular 4.4
I feel where plastic CUs are concerned, we have little choice but to C3 as an absolute minimum. If Regulation 421.1.201 isn't met. ie condition of enclosure in terms of fire rating. Then I will be covering my proverbial. Sometimes I see these schedules as trick question scenarios.
So default Code 3 thankyou IMHO.
As said cover your arse, its your signature.
The condition in terms of fire rating of which "enclosure" are you referring to?
Since January 2016 Amendment No. 3 to BS 7671 (421.1.201)IET Wiring Regulations states that within domestic (household) premises, consumer units and similar switchgear assemblies shall have their enclosures manufactured from non combustible material, or be enclosed in a cabinet or enclosure constructed of non combustible material and comply with product standard BS EN 61439-3.
Not quite sure where a properly fire lined cupboard under the stairs works with BS EN 61439-3
 
As per the eicrs section 4 of the schedules 4.4 the consumer units enclosure itself. Granted if its in a non combustible enclosure then the relevant reg would be satisfied and compliant. But most pre AMD 3 consumer units are simply mounted as installed as indeed they would be. But under those conditions the schedule ie 4.4 leaves you with little choice but to give it some code ie 3. As a plastic c/u by definition is not constructed of non combustible material. IMHO.
 
Thanks for the replies, as said we all have our reasons for coding these things or not coding as we feel fit.
For what its worth, I like most have seen these reports gain page after page as times gone on. In particular the Inspection schedule has become very comprehensive.
So looking at section 4 and in particular 4.4
I feel where plastic CUs are concerned, we have little choice but to C3 as an absolute minimum. If Regulation 421.1.201 isn't met. ie condition of enclosure in terms of fire rating. Then I will be covering my proverbial. Sometimes I see these schedules as trick question scenarios.
So default Code 3 thankyou IMHO.
As said cover your arse, its your signature.
So C3 absolutely as it doesn't 100% comply with 421.1.201 - I understand

So I assume C3 - no question if the installation doesn't comply with 514.4.1 or 514.4.5 as well?

(Cables not coloured blue; brown, black, grey, blue)


Surely if we decide that anything not 100% compliant with the latest standard must be C3 as a minimum, this applies across the board, not just specific areas such as cu's
 
So C3 absolutely as it doesn't 100% comply with 421.1.201 - I understand

So I assume C3 - no question if the installation doesn't comply with 514.4.1 or 514.4.5 as well?

(Cables not coloured blue; brown, black, grey, blue)


Surely if we decide that anything not 100% compliant with the latest standard must be C3 as a minimum, this applies across the board, not just specific areas such as cu's
Its the implications as per the schedule and specifically section 4s 4.4 that leaves you with limited options. Its not about retrospective installations. Ie installs that complied with older versions of BS 7671, not necessarily having to comply with latest versions. Its more specific than that. Its about how you respond and classify to that particular section on consumer units and there enclosures. As said I cant see that the way the eicr phrases that particular section gives you much by way of options. I like most have read it many times, and still come to a C3 conclusion in most instances. But then, thats my view, but always interesting to discuss other viewpoints on this. As said we all need to cover ourselves when signing these things.
 
Its the implications as per the schedule and specifically section 4s 4.4 that leaves you with limited options. Its not about retrospective installations. Ie installs that complied with older versions of BS 7671, not necessarily having to comply with latest versions. Its more specific than that. Its about how you respond and classify to that particular section on consumer units and there enclosures. As said I cant see that the way the eicr phrases that particular section gives you much by way of options. I like most have read it many times, and still come to a C3 conclusion in most instances. But then, thats my view, but always interesting to discuss other viewpoints on this. As said we all need to cover ourselves when signing these things.

Why does it leave you with limited options? 5.1 would leave you with the same options for identification of conductors.

Compliance (or not) with any previous standards does not form part of periodic inspections, the question is: is the installation satisfactory or unsatisfactory? (~ reasonably safe vs unsafe) - the same non-compliance such as premature wiring collapse - it may have been compliant with a previous standard (which is irrelevant) may generate C2, C3, or nothing, - if the cable is unsupported such that failure could cause entrapment - C2 ; if the failure wouldn't case any issue then depending upon the severity it may be C3, or perhaps just an honourable mention.

I see no difference in any other aspect, the plastic cu may be C2, C3, or mention; cable identification perhaps C3 or mention, or nothing at all, cable supports, etc etc.
 
Why does it leave you with limited options? 5.1 would leave you with the same options for identification of conductors.

Compliance (or not) with any previous standards does not form part of periodic inspections, the question is: is the installation satisfactory or unsatisfactory? (~ reasonably safe vs unsafe) - the same non-compliance such as premature wiring collapse - it may have been compliant with a previous standard (which is irrelevant) may generate C2, C3, or nothing, - if the cable is unsupported such that failure could cause entrapment - C2 ; if the failure wouldn't case any issue then depending upon the severity it may be C3, or perhaps just an honourable mention.

I see no difference in any other aspect, the plastic cu may be C2, C3, or mention; cable identification perhaps C3 or mention, or nothing at all, cable supports, etc etc.
We differ in our opinions on this one. I cant see how red and black vs brown and blue can be compared to a consumer unit by virtue of its build material having the ability to contain a fire. So I wouldn't lose any sleep over 5.1. Or not coding it as long as conductors have been correctly connected and identified. And if an electrician has to be warned by a label that an installation contains wiring to 2 versions of BS 7671, then I would question there competence.
Its all about the hows and whys of personal judgements. But I just feel that sometimes, the way these things are written leaves a lot of grey areas.
 
Electrical Safety First best practice guide 4 allows for C2, C3, or no code depending on various factors.
Which is fine as per the best practice guide. But when your filling the schedule of items. Looking at that schedule 4.4 which says and I quote “condition of enclosure IN TERMS OF FIRE RATING” you have to look at your plastic consumer unit hanging nicely in the hallway and decide. Best practice guide or not. Unless the plastic enclosure is itself, within a non combustible enclosure. (Not seen this myself so far) then I stand by a default C3. If you dont and 6 months later the thing goes up in flames. You've covered yourself. Please dont say if connections have been checked then happy days. Ive seen melted main-switches due to contaminated or worn internal contacts not overload or loose connections. Sorry for waffling I just feel you really have to cover yourself from the way these schedules are worded and how they can leave you exposed if you dont think through the hows and whys. Like I say I haven't seen anyone take the trouble to enclose a pre AMD 3 consumer unit in any type of fireproof material. So why take the gamble when a C3 wont effect the EICRs satisfactory outcome. And gives you as the inspector a level of cover that you wont get by not commenting and putting a simple pass against 4.4
 
Which is fine as per the best practice guide. But when your filling the schedule of items. Looking at that schedule 4.4 which says and I quote “condition of enclosure IN TERMS OF FIRE RATING” you have to look at your plastic consumer unit hanging nicely in the hallway and decide. Best practice guide or not. Unless the plastic enclosure is itself, within a non combustible enclosure. (Not seen this myself so far) then I stand by a default C3. If you dont and 6 months later the thing goes up in flames. You've covered yourself. Please dont say if connections have been checked then happy days. Ive seen melted main-switches due to contaminated or worn internal contacts not overload or loose connections. Sorry for waffling I just feel you really have to cover yourself from the way these schedules are worded and how they can leave you exposed if you dont think through the hows and whys. Like I say I haven't seen anyone take the trouble to enclose a pre AMD 3 consumer unit in any type of fireproof material. So why take the gamble when a C3 wont effect the EICRs satisfactory outcome. And gives you as the inspector a level of cover that you wont get by not commenting and putting a simple pass against 4.4
But the point is, this is no different from any other regulation, its not animal farm - all regulations are equal , just that some are more equal than others...

Every regulation has the same standing.

Everyone is able to decide on their level of cya and choose to always give some aspect C3, or C2 that is reasonable.

But as far as the regs go, or the standard forms, every regulation is subject to the same selection of responses, it is up to the inspector to decide which one is most applicable based on the specifics of the installation itself.
 
I tend to follow the BPG and presumably showing that you have followed that would also be a way of covering yourself if something happened - given that terminal damage should always be a C2 (and any loose terminals fixed at the time), and that is the most likely cause of a consumer unit fire...

Having said that I do usually C3 a CU if it's on the escape route or under a wooden staircase - and sometimes add a recommendation that no combustible materials are stored near it.

I agree that there is a subtle difference between ticking the box and the BPG saying 'no code' - they aren't quite the same thing...

However, I also tend to add comments to my certificates to cover things like that there.... with no code, but COMMENT in the Code box. It can also be covered in the comments on condition of installation too.

Though also quite a few of the installations I've inspected are old enough to pass because they are pre-plastic, so it's clearly going to be decades most likely before plastic boards are a rarity, either way...
 
I tend to follow the BPG and presumably showing that you have followed that would also be a way of covering yourself if something happened - given that terminal damage should always be a C2 (and any loose terminals fixed at the time), and that is the most likely cause of a consumer unit fire...

Having said that I do usually C3 a CU if it's on the escape route or under a wooden staircase - and sometimes add a recommendation that no combustible materials are stored near it.

I agree that there is a subtle difference between ticking the box and the BPG saying 'no code' - they aren't quite the same thing...

However, I also tend to add comments to my certificates to cover things like that there.... with no code, but COMMENT in the Code box. It can also be covered in the comments on condition of installation too.

Though also quite a few of the installations I've inspected are old enough to pass because they are pre-plastic, so it's clearly going to be decades most likely before plastic boards are a rarity, either way...
I agree I think the bpg is a fair balance, as is the napit guide, I don't agree with all recommendations, especially the napit, but overall OK - I agree with the comments aspect as well.
 
In the end it really is down to you. Its your name on the report, so your decision to make. Nappits codebreakers does like to make use of code 2s, more so than the Nic from what Ive seen. Is that a bad thing though. ?? I guess with all these EICRs flying around, time will tell.
 
You can't not give it a code if you're doing a BS 7671 compliant EICR, as there's an explicit item in the Schedule

Condition of enclosure(s) in terms of fire rating etc (421.1.6; 421.1.201; 526.5)

So you have no choice about whether or not to compare the enclosure of a CU with the requirements for non-combustibility in 421.1.201.

C2/C3 is the debate, but it has to be one or t'other.
 
I find it interesting that we focus on CUs being non-plastic and yet permit things like REC2 Isolators (with or without SPD) and Thier assemblies to be plastic,
I know - it's bonkers - how can anyone say that it's not "similar switchgear"? Some makers, e.g. Lewden, do SPD isolators in metal enclosures (although theirs could usefully be improved with terminal positions and bus-bar interconnections a la REC2SPD).

But then, you say we "permit" them. Nobody has to - they could code a plastic isolator just like they would a plastic CU.
 
I cant see how red and black vs brown and blue can be compared to a consumer unit by virtue of its build material having the ability to contain a fire.
It can't.


So I wouldn't lose any sleep over 5.1. Or not coding it as long as conductors have been correctly connected and identified.
Again, though, not coding it is not an option.

In the schedule:

Identification of conductors (514.3.1)

And 514.3.1 says (with my emphasis)

......cores of cables shall be identified by:
(i) colour as required by Regulation 514.4 and/or
(ii) letters and/or numbers as required by Regulation 514.5

It's a particularly egregious example of why it was wrong to remove C4.


And if an electrician has to be warned by a label that an installation contains wiring to 2 versions of BS 7671, then I would question there competence.
Take a closer look at my avatar ?
 
C3 by default is understandable (afterall the code is defined as Improvement Recommended); if nothing else it's arse-covering and doesn't fail the EICR; Much like any other nonconformities to current 18th edition; C3 so it's on record in more than just a 'passing comment' and is inkeeping with the purpose of the C3 code - obviously go further attaching relevant regs from 7681, EAWR and that like where appropriate to further explain your engineering judgement.

I find it interesting that we focus on CUs being non-plastic and yet permit things like REC2 Isolators (with or without SPD) and Thier assemblies to be plastic, along with adaptable boxes, for that main being plastic - I believe 5839 makes an stipulation that any junction boxes et all are to be metalic to ensure system integrity bit would have to find out the relevant clauses to confirm.
BS 5839 also requires the connectors to be ceramic (i.e. porcelain) in the junction boxes.
 
You can't not give it a code if you're doing a BS 7671 compliant EICR, as there's an explicit item in the Schedule

Condition of enclosure(s) in terms of fire rating etc (421.1.6; 421.1.201; 526.5)

So you have no choice about whether or not to compare the enclosure of a CU with the requirements for non-combustibility in 421.1.201.

C2/C3 is the debate, but it has to be one or t'other.
For the schedule of inspections, the choices are Pass, C1, C2, C3, Lim, N/V, N/A.
For this particular item, BPG suggests coding either No code (Pass), C2, or C3.
Notice I use the word "suggests". It's ultimately up to the inspector to decide.
 
There are many guides produced by many organisations which contain much guidance, none of it having any authoritative relationship to actual requirements in the regs.

So consider this plastic CU.

  1. Is it non-combustible wrt 421.1.201? If no then it does not comply, so it cannot be a "pass". It just cannot.
  2. C1/C2/C3 - it can be one of those.
  3. LIM - what limitation can you justify for not inspecting the CU?
  4. N/V - how do you justify not verifying the condition of the CU?
  5. N/A - why would it not be applicable to verify the condition of the CU?
 
There are many guides produced by many organisations which contain much guidance, none of it having any authoritative relationship to actual requirements in the regs.

So consider this plastic CU.

  1. Is it non-combustible wrt 421.1.201? If no then it does not comply, so it cannot be a "pass". It just cannot.
  2. C1/C2/C3 - it can be one of those.
  3. LIM - what limitation can you justify for not inspecting the CU?
  4. N/V - how do you justify not verifying the condition of the CU?
  5. N/A - why would it not be applicable to verify the condition of the CU?
I was just replying to your blanket statement that we have no choice, it's either C2 or C3, one or the other, you said...

Also, as an NICEIC Approved Contractor registered on the list of electricians approved to do EICRs, I had to agree to be guided by the BPG 4.
 
I was just replying to your blanket statement that we have no choice, it's either C2 or C3, one or the other, you said...
Well, Pass/Acceptable, LIM, N/V, and N/A I was discounting, as per the above, and C1 I was ignoring as that really implies something more than just a plastic box, e.g. the busbar sticking out of a gaping hole.

I still say that for a CU where there is nothing "wrong" with it, which is what I inferred (so apologies if it wasn't what you implied), C2 or C3 is all there is.

Also, as an NICEIC Approved Contractor registered on the list of electricians approved to do EICRs, I had to agree to be guided by the BPG 4.
Does "guided by" mean "slavishly follow"? Can NICIEC really make you say that a CU which does not comply with the combustibility requirements in the Wiring Regulations is acceptable?
 
Well, Pass/Acceptable, LIM, N/V, and N/A I was discounting, as per the above, and C1 I was ignoring as that really implies something more than just a plastic box, e.g. the busbar sticking out of a gaping hole.

I still say that for a CU where there is nothing "wrong" with it, which is what I inferred (so apologies if it wasn't what you implied), C2 or C3 is all there is.


Does "guided by" mean "slavishly follow"? Can NICIEC really make you say that a CU which does not comply with the combustibility requirements in the Wiring Regulations is acceptable?
No it means guided by.
The actuality is that I almost always code a plastic consumer unit as C3. I also always note it in the comments box. I will sometimes give a recommendation by email that it would be beneficial to upgrade the consumer unit, depending on what all the related factors point to. If it warrants a C2 it gets a C2.

I was just pointing out that guidance from official bodies whose membership includes those who write the regulations is there for a reason and should not be dismissed outright. As you suggest, nor should it be slavishly followed.

All of this type of discussion around EICR coding can be helpful to those new to inspection and testing. However I still stand by what I have said several times on this subject, that those doing inspection and testing need experience of the type of installation that they're inspecting, and if they lack the necessary experience, they should not be doing it. But they are. Hence the plethora of bad EICRs we're seeing being churned out.
 
There are many guides produced by many organisations which contain much guidance, none of it having any authoritative relationship to actual requirements in the regs.

So consider this plastic CU.

  1. Is it non-combustible wrt 421.1.201? If no then it does not comply, so it cannot be a "pass". It just cannot.
  2. C1/C2/C3 - it can be one of those.
  3. LIM - what limitation can you justify for not inspecting the CU?
  4. N/V - how do you justify not verifying the condition of the CU?
  5. N/A - why would it not be applicable to verify the condition of the CU?
Hitting the nail right on the head. And my exact point, that its the Inspection schedules wording regarding Section 4 specifically 4.4 That asks you to Judge the consumer unit enclosure in term of fire rating and quoting regulation 421.1.201. That as I have said, takes the judgement away from you and leaves you with no option but to provide a code against a stand alone plastic consumer unit relying on its own enclosure. with C3 at best. When in reality a well installed dual RCD unit (as an example) would probably have bugger all wrong with it, and give many years of trouble free service, as they often do. But because of the way these report schedules are phrased, and to ensure you are covering yourself against this, you simply have to code it. Not your choice, or even your opinion necessarily but that's the road your being taken down. So in a nutshell Schedule 4.4 forces you to code even where advisory bodies say under certain conditions it wouldn't be worthy of a code. And that's contradictory advice IMHO.
 
Last edited:
Quoting Electrical Safety First
"What classification code would be appropriate where, post January 2016, an insulated consumer unit is encountered in a domestic premises? If the consumer unit is located under wooden staircase or within a sole route of escape from the premises, a code C3 classification (meaning that improvement is recommended) would be appropriate. If located elsewhere, this might be worthy or not, but it would not be necessary to record this on the condition report."

So does/maybe Inspection schedule 4/4.4 get N/A as per BPG ??
Because the C/U shows no signs of thermal damage, and is not located under a wooden staircase, or within a sole route of escape.
So judged not necessary to record on the condition report.
With a note made to this affect in the comments section.

Just throwing this one out there for comment/opinions.
 
Last edited:
Hitting the nail right on the head. And my exact point, that its the Inspection schedules wording regarding Section 4 specifically 4.4 That asks you to Judge the consumer unit enclosure in term of fire rating and quoting regulation 421.1.201. That as I have said, takes the judgement away from you and leaves you with no option but to provide a code against a stand alone plastic consumer unit relying on its own enclosure. with C3 at best. When in reality a well installed dual RCD unit (as an example) would probably have bugger all wrong with it, and give many years of trouble free service, as they often do. But because of the way these report schedules are phrased, and to ensure you are covering yourself against this, you simply have to code it. Not your choice, or even your opinion necessarily but that's the road your being taken down. So in a nutshell Schedule 4.4 forces you to code even where advisory bodies say under certain conditions it wouldn't be worthy of a code. And that's contradictory advice IMHO.
No, there is nothing that takes judgement away from the inspector, the example schedule in appendix 6 is merely a generic example, many on-line tools differ quite significantly, they only have to be based on the example, not rigid to it.

This is noted in 651

You don't need to include things that don't comply with the latest regs, only those which don't comply, which may give rise to danger.

The reporting is all based around what has been tested/inspected and anything that leads towards a dangerous condition
 
Quoting Electrical Safety First
"What classification code would be appropriate where, post January 2016, an insulated consumer unit is encountered in a domestic premises? If the consumer unit is located under wooden staircase or within a sole route of escape from the premises, a code C3 classification (meaning that improvement is recommended) would be appropriate. If located elsewhere, this might be worthy or not, but it would not be necessary to record this on the condition report."

So does/maybe Inspection schedule 4/4.4 get N/A as per BPG ??
Because the C/U shows no signs of thermal damage, and is not located under a wooden staircase, or within a sole route of escape.
So judged not necessary to record on the condition report.
With a note made to this affect in the comments section.

Just throwing this one out there for comment/opinions.
This is probably a case where the old C4 would have been more appropriate really - it is not compliant with current regulations but doesn't in many cases need a recommendation to upgrade (as long as well installed etc in a safe place, etc.).

N/A is arguably more appropriate than a PASS, if it's not being coded.... With a comment in the inspection schedule alongside it or in the observations page.
 
Quoting Electrical Safety First
"What classification code would be appropriate where, post January 2016, an insulated consumer unit is encountered in a domestic premises? If the consumer unit is located under wooden staircase or within a sole route of escape from the premises, a code C3 classification (meaning that improvement is recommended) would be appropriate. If located elsewhere, this might be worthy or not, but it would not be necessary to record this on the condition report."

So does/maybe Inspection schedule 4/4.4 get N/A as per BPG ??
Because the C/U shows no signs of thermal damage, and is not located under a wooden staircase, or within a sole route of escape.
So judged not necessary to record on the condition report.
With a note made to this affect in the comments section.

Just throwing this one out there for comment/opinions.
That is exactly my understanding.

As highlighted previously, in effect C4 showed something was non-compliant, but did not represent a danger; such a condition would be appropriate here.

It was basically removed because users would see this and think it needs to be addressed, which is an issue with putting C3 on the report, many would see it as "not a clean report" so needs to be sorted.
 
That is exactly my understanding.

As highlighted previously, in effect C4 showed something was non-compliant, but did not represent a danger; such a condition would be appropriate here.

It was basically removed because users would see this and think it needs to be addressed, which is an issue with putting C3 on the report, many would see it as "not a clean report" so needs to be sorted.
So are we saying provided the plastic C/U satisfies certain criteria regarding thermal damage and location. And because it was designed pre AMD 3 of the 17th. The inspection Schedule section 4 ref 4.4 would not be applicable in this instance. ??
As an example !!
If you own a classic car, there is no legal obligation for it to be fitted with seat belts. And yet these days its considered a major safety requirement and more so, a legal requirement.
Not an exact comparison, but in principle !!
 
Last edited:
So are we saying provided the plastic C/U satisfies certain criteria regarding thermal damage and location. And because it was designed pre AMD 3 of the 17th. The inspection Schedule section 4 ref 4.4 would not be applicable in this instance. ??
As an example !!
If you own a classic car, there is no legal obligation for it to be fitted with seat belts. And yet these days its considered a major safety requirement and more so, a legal requirement.
Not an exact comparison, but in principle !!

The problem with the car/seat belt analogy is that OEM seat belts aren't readily available for most classic or vintage cars, whereas replacement metal consumer units are.
 

Reply to Plastic consumer units and how to code them in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
936
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
703
Hello engineers. I did EICR in two bed rented flat in a block of flats. There is old plastic fuseboard just above the entry door. There are only...
Replies
19
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock