Search the forum,

Discuss Please put my mind at rest in the UK Electrical Forum area at ElectriciansForums.net

H

Hottub

hi guys I have had an electrician come and put some wiring in ready for a hot tub delivery.

I passed on a electrical document sent to me by the hot tub company which had 6mm on it.

He has run a armoured 2.5mm 3 core cable from the main board and a dedicated 32amp mcb to an external rotary switch ( about 3 metres away ) also 32amp. From the switch he has run the same 2.5m 3 core around to where the hot tub will be ready to be connected ( no more than 4m away ).

He says its more than enough but as I've seen 6mm on the wiring diagram I'm worried.

So shall I stop worrying? Or demand he use 6mm? Or find a different sparky?

Thank you for your time.
 
it may well be that 2.5mm cable is adequate for the load, but the rating of the MCB should be below the design current, unless he's working on the principal that the tub is a fixed load and thus can dispense with overload protection. tin hat ready.
 
Seems very odd that he knows the rating of the hot tub then either totally miscalculates or is not competent.
 
all boils down to this:

1. what is the load current of the hot tub? get that from rating plate.
2. from the above, what size cable is required? from BS7671.
3. from the size of the cable, what rating should the OCPD be? Ib<In<Iz.

simpleesss.
 
Get the, cough, splutter, spark back to change the heating element for a less powerful one and have a warm tub instead! Saves on your leccy bill that way!!
Seriously though, it is a poor show that they fitted 2.5mm if they knew the rating of the hot tub first.
 
Firstly, I recall 2.5mm swa has a higher rating than 27 amps.

Has said spark been paid? Has he provided you with an electrical installation certificate? A commitment to notify under part P?
 
2.5mm thermosetting SWA has a current rating of around 36a clipped direct from memory...I don't have the BYB to hand. So a 32a OCPD device may be acceptable depending on installation method. The problem may be volt drop or 90 degree terminations, depending on the actual load being drawn, and manufacturers instruction. I think you are all jumping the gun somewhat stating this is wrong without all the info. BTW I've added a disagree to post #3 because it's misleading, there are instances where a 2.5mm conductor will be protected by a 32a OCPD. That said in practice I'd never use a 2.5mm based on the info given either. I don't think any of us would install a 2.5mm in this situation.
 
Last edited by a moderator:
The M.I should also contain details of a suitable OCPD,which if the cable size is 6mm,would be euro-ish. Most older units came with American wire sizing and protection device information.

There are some variables,and lee-way,in the OP's set-up,but would require more specification,and maybe assessment of current during use.....but it hasn't landed yet,has it....;)
 
I'd also add that it seems unlikely that the actual load will be over 30a given that the OP has indicated a 3kw heater, I cant see a filter pump adding that much, where's the rest coming from?
I agree, I can't remember the details but a while back I installed a piece of kit that had an operating rating of 2.7kw yet the manufacturers instructions "recommend" a 6mm supply cable. But it did say something along the lines of " This machine should be installed by a qualified electrician and in accordance with the wiring regulations"
Without all the relevant information its difficult to make a proper judgement call.
 
The MIs are there as a guide, how can they specify the csa of a supply cable when they have absolutely have no idea of the installation. I suspect they say 6mm because that's what would be needed if run in T&E in insulation. Suppose the hot tub was 200m away, would 6mm be acceptable then?
It's up to the electrician to design the installation.
 
Worked on quite a few tubs where the recommended supply was 6mm² and 32A the reality being with the heater and all pumps running they rarely run above 18 - 20A although the inrush starting the pumps does give a short current spike
 
Good points made by Wirepuller. I was blindly thinking of 2.5mm T&E max being approx 27A, but obviously different cable types have differing CCCs.
 

Reply to Please put my mind at rest in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning. Needed some advice please. I am getting an AC condenser unit installed on an outer bedroom wall but only after some internal...
Replies
4
Views
964
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
514
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock