Right lads here is one for the books!!

Tns or Tncs. :)
519d9e6d-25b6-8b67.jpg

519d9e6d-25c8-7410.jpg
 
Yhea that happens more than you would think makes filling out the test form tricky.

In fact I have exactly that situation in my own house!
 
The property was originally TNS at some point

When it got renovated I highlighted the lack of proper earth as the clamps had come away from the cable sheaths at the head.

Nedl said and it would be better if upgraded to PME as the network had been recently upgraded in that area

I agreed as landlord was paying for it!!

Just surprised me as to why they bonded to the sheath!! I'm not fussed as it goes down on paper as PME

Never seen it done , normally one or other!
 
Disconnect the sheath bonding cables!!!! From your explanation, this DNO cable is also supplying TN-S earthing to other customers.

Whoever from the DNO that connected the sheaths to a PME connection needs bloody shooting... The two systems need to be kept separate when the cable is in progress of being PME'd....
 
If you call it by the old description PME (protective multiple earthing) it makes more sense. For safety, in case the neutral becomes open circuit in the distributors network the neutral is "earthed" at "multiple" points along its run. I can see no issue with this arrangement that you show although it is a little unusual. I would call it T-N-C-S.
 
This type of earthing is called TN-C-S or PME, and should be recorded as such. As you should be aware, the neutral conductor is tied down to earth at every joint made underground by your DNO. Although not widely adopted until the 70's the introduction of PME was piloted in the 1930's. It saved the REC's (at the time) hundreds of thousands of pounds overnight by changing from split concentric, and others, to concentric.
I could be wrong. Am I missing something? I'm open to discussion!
 

Reply to Please tell me what earth system this is!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Right or wrong please? , if wrong, what needs to be done to fix it? thanks in advance.
Replies
13
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
756
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
324

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock