Discuss PME systems and sub mains? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

Staffie

Was working on an installation a few weeks ago (PME domestic) which had a sub to a garage which in turn had another sub which supplied a c/u in a shed about 20 meters down the garden.

Got talking to mate of mine on Saturday who said that both the subs should be protected by an an individual earth electrode?

This got me thinking that I'm sure I did read not so long ago, can't remember where, that the means of earthing on a PME should not be taken out of the equipotential zone, exactly what my mate had said?!

He didn't seem to know why, we both stood in the middle Morrison's both somewhat confused?(nothing new there)

I can only assume that this has something to do with the declared Ze only being applicable at the customers intake only?

Advice appreciated!

;)
 
When you take a supply to a shed, garage or similar out building you must only export the phase and neutral, not the earth. The earth at the new installation EG garage must use an earth rod. If you did export the earth to the garage and you step out of the garage holding onto part of the earthed metal-work, there is the potential to get a belt to earth. This is because there may be a potential difference between earth at the house and earth at the garage earth! Sad but true..
 
When you take a supply to a shed, garage or similar out building you must only export the phase and neutral, not the earth. The earth at the new installation EG garage must use an earth rod. If you did export the earth to the garage and you step out of the garage holding onto part of the earthed metal-work, there is the potential to get a belt to earth. This is because there may be a potential difference between earth at the house and earth at the garage earth! Sad but true..


Thanks mate, that makes sense! I must admit, I've never stuck one in and the spark who did the install on this particular job hasn't either!

So, if the garage was part of the fabric of the dwellings, I take it you may export the earth with the P&N?

;)
 
Thanks mate, that makes sense! I must admit, I've never stuck one in and the spark who did the install on this particular job hasn't either!

So, if the garage was part of the fabric of the dwellings, I take it you may export the earth with the P&N?

;)

yes you can export the earth, because its part of the eqipotential zone.:)
otherwise, if its disengaged from the dwelling, convert to a TT system.:(
 
Had a chat with niceic not long back regading exporting the earth on a PME system. They never use to allow it, but after a meeting with themselves and the IEE they now say its allowed.
 
Had a chat with niceic not long back regading exporting the earth on a PME system. They never use to allow it, but after a meeting with themselves and the IEE they now say its allowed.

Can that be found in writing anywhere? The inspector that may go to one of our jobs may never have been informed, argue with you and say to put right with an earth rod, as he knows best....
 
Hi.

Hi.

A PME system can be exported provided that the either of the following 2 conditions are met

1. There are no extraneous conductive parts within the outbuilding i.e steel frame, water service, gas service etc.

2. If there are conductive parts, then the equipotential zone needs to be extended to the outbuilding via main equipotential bonding conductors sized accordingly i.e a minimum of 10mm2 for each service back to the MET within the house, unless the sub-main is greater than 10mm2 itself.


Personally if there are conductive parts within the outbuilding then I always TT regardless of sub-main size.

Hope this helps.
 

Reply to PME systems and sub mains? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
442
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
The other night, neighbour knocked my door. She said she'd gone to use their outdoor tap, and she thought she'd got a shock. Went and had a look...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock