Hi guys,

I've just completed a job in moving 14 plastic / rubber injection moulding machines from their old factory up to their new unit, most have been supplied with 100A / 125A fuses from the busbar down to a local ISO and into the machine just to give an idea of the size of the install. Half of them could've been supplied by 63A / 80A to be fair but I had lots of 35mm 4 core laying around to use :)

My question is this.....

There was an old PFC unit that they want re-installing into the new building, but how do I figure out that it's actually suitable / efficient if I do install it?

Half the machines don't have details and 5 of them are stepped down to 110V with their own local transformers.


Cheers for any help in advance peeps
 
Go and hire in a 3 phase power anlayzer, do a 24h / 7d day power quality survey at the main meter position. This will let you know if PF correction is required, the kit will also tell you if the PF unit still works, see what happens when you turn it off and on at light load.
 

Cheers I'll give them a call once I know what I want.

I have a few pics of what came out and what it's going into. Because the new factory main supply has been terminated with two single cores run in parallel, the existing clamp meter won't fit round the two cores. Can I get a new clamp to suit and wire it back to the new unit? If so what is it that I'm looking for?

https://www.dropbox.com/s/brfzzbtfa5mhtes/image1.JPG?dl=0

https://www.dropbox.com/s/hkkb106xnc1uhwt/image2.JPG?dl=0

https://www.dropbox.com/s/0ynwpyy05kjb6yc/IMG_4042.JPG?dl=0
 
A reasonable starting point might be that the existing PFC was correctly sized and should be good for the relocated equipment.
 

Reply to Power factor correction units in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi there Complete novice electrical wise. I am refurbishing an old 1950s Injection Moulding machine and looking to replace the Power Timer...
Replies
55
Views
6K
Hi, Ive got an upcoming job to determine the cause of a BS88 fuse tripping in a switched fuse unit that powers a 125A consumer unit yet none of...
Replies
3
Views
908
Hey everyone, lately I've been trying almost everything to reduce the electrical noise over my Be Quiet Straight Power 11 850W 80+ Platinum PSU...
Replies
7
Views
2K
Hi guys and girls, I'm newly qualified and want to confirm my method is sound before I commence any work. I'm registered with my CPS so can...
Replies
15
Views
10K
I've just carried out a periodic inspection on a building on an old RAF/USAF site. Commercial single story building. Wiring system is around...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock