Hello, hello, long time listner, first time caller...

So, I have an issue in a house I'm trying to get ready to rent. The plumber has installed a power shower despite my asking him to install a mixer type. He's not gonna come back and fix it, and I havent paid for shower.

The issue I have is getting power to the thing. I've literally just had it carpeted so really dont want to be ripping them up, and dont want to have to retile the bathroom. Then someone suggested running power around the outside. The house is an end terrace, and the consumer unit is on an outside wall. I'm wondering if there is anything in the regs that would prevent me running a high csa flex around the outside and drilling thru the wall at each end??

Around 14m run and 8.5kw, I make it 6mm2 flex

All help gratefully recieved

Regards

Milo
 
H07RN-F flex with ferrules on the ends would be acceptable if it is adequately supported and not at risk of damage as it is outdoor/UV resistant. NYY-J is stiffer and tends to sit better, and no need for ferrules.

One thing about going out through a wall and along is to take care of the cable's minimum bend radius. Typically that is 6-8 times the cable diameter and for 6mm 3C it ends up about 10cm, i.e. think of wrapping around a 20cm / 8" diameter pipe. It is big by wall exit standards!

Using some 25mm PVC conduit outside and 6mm T&E might be better as it can bend tighter in the "flat direction" if done with care to line up that way. The conduit would protect against UV light and looks nice and straight (assuming well installed with support saddles at sensible intervals). Something like these at the two ends so the cable can exit through the centre it to the wall's hole:
 
You wanted a mixer, so why can’t another plumber supply and install a mixer?

It might be a simpler solution than external wiring.

The circuit would require rcd protection and need to go through an isolator at the bathroom before the shower. Plus working at height outside…
 
The plumber has installed a power shower despite my asking him to install a mixer type.
I assume that your DHW is heated with a gas boiler? If so, remember that electricity is more than 3 times the cost of gas, so you'll be paying £££ for the plumber's mistake every time you have a shower.

I totally agree with Littlespark.
You wanted a mixer, so why can’t another plumber supply and install a mixer?

It might be a simpler solution than external wiring.
 

Reply to Power Shower Feed, external run legal?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
Morning All, I am looking for advice on what KVA I need to advise UKPN so that can quote for new supply to a greenfield site, the requirements...
Replies
3
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Doing an EICR today and customer has a tumble dryer in the shower room. Room is an L shape with shower directly in front of door and around...
Replies
10
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock