Discuss Power transmission 300 KW over 1.8 KM in the UK Electrical Forum area at ElectriciansForums.net

gaz101

-
Reaction score
11
Hi all
: fairly strange question has anybody dealt with any companies that know about sending this sort of power over 1.8 or slightly more kilometres all over private land
Customer wants to transmit privately generated power from one site to another are there any companies that specialise in this sort of thing?

400V at each end
 
Lots of companies supply the national grid with stuff just like that.
300kw is quite small scale and the investment may take a while to recoup
 
You are only going to get a sane solution by going to HV along the route as at 400V you would be looking at something crazy like 2500mm^2 cable!

Cheapest would be poles for the HV run but depending on the location that might not be acceptable.
 

Reply to Power transmission 300 KW over 1.8 KM in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
706
I have a question for you all, We recently moved, and the old house had the analog meter on it, the new place has 3 structures on the property.. a...
Replies
10
Views
3K
S
Hello, Sorry if this isn't the right forum for this. Didn't look to be far off... So I'm looking for some advice please with regards to...
Replies
13
Views
1K
E
If you want to save on your monthly electric bill and reduce your greenhouse gas emissions at the same time, you might buy a new, energy-efficient...
Replies
0
Views
986
Electricity News --
E
Hi All got call out to a domestic fault on consumer unit totally separate from the job & client mentions to me that they had Battery storage...
Replies
30
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock