Discuss Preferred method of installation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Rappid

-
Reaction score
49
Had a look at a job the other day, client has brought a MK RCD Garage CU and wants it connected up.
Supply is TNC-S with a 100mA RCCB protecting a BS1361 fuse board which has MCB's

Option 1. Replace the RCCB with a time delayed RCD and connect garage CU to new RCD

Option 2. Henley block the meter tails and connect both CU's to Henley block so both RCD's are in parallel

All wiring will be surface mounted SWA.

Both methods would achieve discrimination, which method would be the preferred one?


Thanks
 
Had a look at a job the other day, client has brought a MK RCD Garage CU and wants it connected up.
Supply is TNC-S with a 100mA RCCB protecting a BS1361 fuse board which has MCB's Are you sure this is a TNC-S system, if so why as it got this 100mA RCCB

Option 1. Replace the RCCB with a time delayed RCD and connect garage CU to new RCD Expensive.

Option 2. Henley block the meter tails and connect both CU's to Henley block so both RCD's are in parallel

All wiring will be surface mounted SWA.

Both methods would achieve discrimination, which method would be the preferred one?


Thanks

Here is my take on things, Was the system originally TT and been converted to TNC-S and the RCCB never removed. If indeed it is a TNC-S, then, check your Ze reading and if it is a TNC-S then you can redesign your install
 
Last edited:
Thanks Malcolm

I did suspect it was a TT system but unable to find a connection to a earth rod. It looks like the electricity board converted to a TNC-S when they put a new meter in, they also changed tails to 25mm.
 
Tested the Ze, got a reading of 0.36 ohms :banghead: cleaned and tightened the contacts and got 0.35 ohms :cheesy: it's not ideal.

The RCCB is still operational.
 

Reply to Preferred method of installation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
458
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
492
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
755
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock