So I had my yearly assessment today with my friendly local engineer. He was fair enough but there was 2 points he pulled me on that have niggled me because I am sure I was right.
Would like some other opinions please.

Firstly a 60 Amp TN-S supply to a domestic property. ... what is the minimum size tails?
Secondly do you guys tick the double insulated box in S.O.I because of the meter tails?

I'll let you know who was in each corner after a few replies so as not to sway your decision ( as if it could)
 
First one depends on the load that you have calculated for the installation.

Second one I don't agree with. Tails are insulated and sheathed, same as twin and earth...

Edit: Speedy Lee beat me to it!
 
I installed 25mm tails to a db in the garage around 1 meter from meter/cut out.
Was told the db could be hit by a larger car (whatever that means) and I should have moved the db with a switch fuse isolator and coming out to other side of garage with a 35mm swa 2core and 16mm cpc.
I asked my QS why 35mm as volt drop wasn't an issue, he said had better mechanical strength haha!!
 
Last edited:
Theoretically the minimum size tails for a 60A fuse would be 10mm² as this can take 64A when clipped direct (and tails are often in free air). I would tend to use 16mm² as the fuse may often be 60/80A labelled so I could not be sure of the protective rating.

For the schedule of inspections the protective measure for meter tails is ADS, by chance the cable could be classified as equivalent to double insulated, but the sole protective measure is not double insulation, it is ADS. If if it were double insulation then there would be no fuse required and no earthing required.

Now worried about the quality of the assessors if their reference books are just the OSG.
 
Double insulation means TWO layers of insulation or a single layer of reinforced insulation so in your case it doesn't apply. Those conductors have one layer of insulation and an overall sheath for mechanical protection.
Need to stand your ground with these people.
 
16mm tails on existing install... 25mm tails on a new install (both with 60A main fuse)

i.e. I wouldn't upgrade the 16mm tails to 25mm on an existing install with a 60A fuse.
 
My thoughts on clipped direct is that it may apply between the head and meter where there is no enclosure, enter them into a board they are no longer clipped direct and should be down rated.
 

Reply to Pretty sure my cps assessor was wrong in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am looking to join a CPS. I have looked at NIC Napit and Blue Flame. Just for a small cost difference Napit a Nic look to be a better option...
Replies
14
Views
3K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
Replies
6
Views
1K
In addition to the 4 main, well known competent persons schemes (NICEIC, ELECSA, NAPIT and STROMA), there is apparently another, lesser known...
Replies
18
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock