TNCS system am I mad went to a house today PME system PSCC and PEFC are supposed to be the same got 4.8kA at main switch and when I did the PEFC I got 7.1kA is this correct and if not what would cause it.

Thanks in advance.



Chris

Sorted just tried the same tests at home looks like my meter may need to go into early retirement
 
Last edited by a moderator:
Megger 1552 readings at home are all over the place as well one minute its 5.1kA kick the dog and cat go back test again and its 7.5kA. Pets know whats coming they run off I go back and check and its back to 5.1kA.

Uo/Ze gives me 7.6Ka


Chris

PS 10volts on meter battery check
 
TNCS system am I mad went to a house today PME system PSCC and PEFC are supposed to be the same got 4.8kA at main switch and when I did the PEFC I got 7.1kA is this correct and if not what would cause it.

Thanks in advance.



Chris

Sorted just tried the same tests at home looks like my meter may need to go into early retirement

was the earthing conductor connected when you did the pscc? if not if not the test would not have included parr earth paths but pefc would which could increase the ka reading
 
Were you using the standard Megger croc clips? I've found these a bit iffy when testing - they quite often need a good squeeze onto the cables to make a good connection.
 
I have very limited experiance but I thought pssc and pefc are usually different by how much I don't lmow but usually I find one to be about 0.34ka and one to be about 0.36ka but this is at my training college so not sure about reall world.

And you just record the higest one as your PFC I belive?.
 

Reply to Pscc = pefc ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
675
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
551
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock