Discuss Pulling 16mm SWA through 150 M of conduit? in the UK Electrical Forum area at ElectriciansForums.net

1Justin

-
Arms
Reaction score
157
Would you attempt to pull 16mm SWA through 150M of existing underground conduit?

A potential job I have taken a look at. I would need to be very sure I could get it through before shelling out £££ on that much cable! (- I already advised the Customer it would have made much more sense to install a cable before filling the trench!).

Facts:
-Conduit was laid about 1 year ago. It is 50mm dia corrugated plastic type, laid in 3 sections of 50M. - I have no idea of the quality and continuity of the two joints, but the Customer will ask the contractor who laid it in.
-Conduit ~ 600mm deep through a semi-wooded garden, no special precautions such as gravel layer or warning tapes.
-Laid pretty straight for first ~60M, then takes a gentle curve perhaps 20 foot radius and turns total about 60 degrees before the end.
-String is through already to start proceedings, so I would be investing first in lots of cord, and a damn great length of blue rope.
-150M of 16mm will weigh about 150Kg!
- I also am aware it only takes a little bit of mud to make a nice plug!


Questions:
Termination for cable nose and ways to stop it snagging?
Friction being the enemy, - so Lubrication?
Best way to fix cable to rope?
Will I need a tractor ...??? :eek: (- AKA how hard can you pull safely?)
I haven't seen any longer than 100M from distributors. - Can longer single lengths be got?

Homework:
Ongoing decision as to whether I can get away with 16mm anyhow, but that's work in progress, and not my question here.
 
Not a chance. That's a tiny ducting.

You should be fastening on with a small cable sock or a series of hitches tied on rope.... neither of which will fit down this ducting easily I reckon.

Which idiot put in such a small duct with no pulling pots ? If it does fit down you are gonna be digging it out in a couple of places.
 
so, even if you can manage it, how's it going to comply without digging a trench to fit warning tape? i'd run away from this one.
 
Well I suspect the danger of damaging the cable would be quite high?... Stretching it and the like if you used a tractor. If you can't do it by grunt power I'd say it needs to be dug up again.
and yeah as andy said, a cable sock or hitches, and I'd probably use hitches on preference as you could hitch it for 20 odd meters on the cable to ensure it doesn't come loose half way through the pull......
And I would also be trying to secure a rope on the entry end of the cable I case the worst happens and you break the pulling rope! At least you may be able to pull it back! Lol.
 
As already stated, be far easier if there was some pits where you could pull a loop. That's a hell of a long pull. Even with a securely hitched on rope, plenty of lube, the sheer drag alone would make it a b****rd of a job.

Not planning to do it on your own are you??

Be inclined to give that a miss I think.
 
I'd dig the duct up every 30 meters and pull it in sections. Whatever you do don't give them a guaranteed price or quote, this type of unknown installation would be hourly/daily rate only.
 
it will fit... just.
as andy says a few half hitches and plenty tape.
but it will be a bit of a pull thats assured. a 75mm duct would have been better.
yes you can get swa in lengths longer than 100m.
do your homework on the cable size as that is a fair distance.
tractors and the like tend to stretch the cable. manpower is unfortunately the way to go.
hire a set of jacks if you can for the cable to roll off.
best of british
 
Whoa. Pretty much as common sense has been shouting to me then! ie -damn near impossible, with a hint of encouragement from Dcf..

I have made no commitment to the Customer and I did suggest the possibility of needing to re-dig. I also said I'd work this one on a day rate! Recon i'll need some mates who've been eating plenty of spinach as well.

Any more opinions gratefully received.
 
If you are going for it...practice your knots. Particularly the hitches around the swa.

Also as suggested hire or borrow some cable jacks and its worth while using a couple of short scaffold poles and clips to prevent the whole lot tipping forward as it gets lighter.
 
Although you are doing totally the right thing by pricing by the hour , I think you will be OK with the help of 3 or 4 others to help you .You do not say how many cores the cable will be , but even a 5 core 16mm will fit all be it some what snugly . Don't forget to meter out the cable as it is pulled so that you know where to dig and break in to the duct if needed ! You say it is in semi woodland , so I assume digging will not make much of a scar if the need arises . You should be able to borrow a set of jacks from your wholesales if you have none and a sock would be good but blue BT rope will do , I would not go to far along the cable with the knots though as this is where the dreaded friction will be the worst . With one person feeding it in to the duct , (and I mean feeding ! ) and 3 or 4 pulling you will be surprised what you can move .
 
Last edited:
Goodluck.

Last cable i pulled in was not fun, it might only have been network cable but in old ducting, no rope and existing cables made it a basterd.

It should have been easy and it was till last bit.
 
I like the poll! :juggle:

I was kind of thinking some sort of steel cable grabber might make for a slimmer hold on the SWA. Maybe rather than knotting the rope over, I make up a swaged steel cable with half a dozen little steel cable lassos on it and grab it with that.

- Then maybe some kind of hat (perhaps a steel pipe with a conical/reduced front end) on the front cable end to help exit the pull cable axially. I could also swage the rope loop to that which would avoid any bulky rope knots...

The conduit is all ridged though.

Lubricant then which won't damage the cable? - Vegetable oil? Tallow?
 
I like the poll! :juggle:

I was kind of thinking some sort of steel cable grabber might make for a slimmer hold on the SWA. Maybe rather than knotting the rope over, I make up a swaged steel cable with half a dozen little steel cable lassos on it and grab it with that.

- Then maybe some kind of hat (perhaps a steel pipe with a conical/reduced front end) on the front cable end to help exit the pull cable axially. I could also swage the rope loop to that which would avoid any bulky rope knots...

The conduit is all ridged though.

Lubricant then which won't damage the cable? - Vegetable oil? Tallow?

Yellow 77?
 
Not having a big swage tool doesn't help.. but if one were to strip off a foot of the SWA, pull all the wires together into a cone and swage a decent sized pull cable to that, it might go as well as can be expected..:lightbulb:.
 
Corrugated plastic pipe, couldn't of chosen a worse design for such a long pull. The other thing is, how strong is this conduit /duct?? Laid at 600mm, if the wall isn't of a sufficient thickness, then there is a good chance the pipe's wall in places could have already collapsed, or starting to collapse, under the weight of the soil.


You're either going to be lucky and the pulling is going to go like a knife through butter, or as i suspect it's going to be a long pull, with one thing cropping up after another and ending up with a stretched cable at the end for all you're trouble. Use plenty of lubricant, ...you're going to need it methinks!! lol!!
 
get another long rope attached to existing rope with a knot that would increase size of rope ( reef knot ? ) and pull through duct and back to see if it snags anywhere before attaching cable
 
1: get some rope and tie a big knot in it just slightly smaller than the duct about 40mm big put tape round it and then pull it right thru the duct not forgetting to attach a new draw rope to it , this will let u know if the duct is ok and not squashed at any point .
2: if it goes thru no bother ^^^ then the job is easy.
3: cable jacks - 3 men - 2 way radios , fairy liquid , one rolling it off the drum , one pushing it into the duct and one NOT pulling the rope to hard but keeping the tension on it .

take turns each , at pushing the cable as its the hardest job .

most likely place to get stuck is the joints so when u tape the nose of the cable make it as round as you can
 
Wouldn't struggle manually pulling it. Hire yourself a cable winch from hss or alike. That length of blue rope with cable and the drag would be a right mare. Winches come with about 300m of steel rope, if you pull the steel thro with the blue rope and then use a cable sock as others have suggested. The beauty of the winches is they are clutched so you have a protection against cable damage. I know it works cos I have recently used one to pull a 25mm through the same size duct as OP after previous spark had walked off site and builder had laid ducts under concrete slab. Winches aren't cheap but job took us about 1 1/2hrs so it was money well spent.
 
am not being cheeky to anyone on this thread but its only a 16mm swa , this aint a big cable , talk of the 50mm duct not being big enough and cable winches and tractors , yes its a long run but if the duct is fine then its not that hard to pull it thru , plenty of lube and take ur time and it would be in in no time
 
am not being cheeky to anyone on this thread but its only a 16mm swa , this aint a big cable , talk of the 50mm duct not being big enough and cable winches and tractors , yes its a long run but if the duct is fine then its not that hard to pull it thru , plenty of lube and take ur time and it would be in in no time

You don't sound cheeky, just inexperienced. The friction alone added to this length of cable is going to make it near impossible, and that's before you factor in the ridged ducting and the small diameter. 150m without pulling pots is crazy talk.
 
Cable pulling through duct over long distances without manhole pull stations is an art in itself. Dead pulling, no-matter whether the SWA is 16mm or far larger is going to end up stretching the cable. As someone pointed out earlier, cables need to be simultaneously fed into the duct while manually or winch pulling cable.

It's also so easy to damage the cables sheath as it enters the ducting, ....as sure as eggs are eggs smooth entry belled duct ends haven't been used at entry and exit points!! In this case you don't even know how the lengths of ducting have been joined underground which could easily also be a source of damage to the cable sheath if there are any rough edges left in the ducting etc!!
 
Unless I am missing something ? How do people think that pulling an armoured cable of this size which is properly secured , by "hand" whilst being fed at the same time is going to stretch it !? It is unusual to get a labourer to put any more effort in to a cable pull than would be required to pull the skin of a semi dried turd , let alone stretch that cable in my humble experience . And before the outcry of inexperience is heard On the last job which required some pulling a couple of weeks ago , 5/6 of us managed to pull in 95m/70mm 4c , 110m/70mm 4c , 120m/120mm 4c , 145m/150mm 4c , 155m/150mm 4c , 170m/150mm 4c , 180m/185mm 4c , I will admit we did use our quad and winch set up on the last three as we were feeling fatigued by then , but all these took the grand total of 8 hours to complete . The thing that would worry me the most about the job is as Engineer54 has said about the unknown state of the ducts.
 
Last edited:
Corrugated plastic pipe, couldn't of chosen a worse design for such a long pull. The other thing is, how strong is this conduit /duct?? Laid at 600mm, if the wall isn't of a sufficient thickness, then there is a good chance the pipe's wall in places could have already collapsed, or starting to collapse, under the weight of the soil.


You're either going to be lucky and the pulling is going to go like a knife through butter, or as i suspect it's going to be a long pull, with one thing cropping up after another and ending up with a stretched cable at the end for all you're trouble. Use plenty of lubricant, ...you're going to need it methinks!! lol!!
its corrugated....so should have held its shape...
 
Let me assure you JD6400, inappropriate or DEAD pulling of any sized SWA cable by inexperienced personnel will result in the cable being stretched, and you can take that to the bank. Use of a suitably sized cable sock and correctly set calibrated cable pulling winch, with cable rollers and a free moving cable drum will in most instances alleviate cable stretching.... Start pulling any cable with any other form of tractor/machine and you'll almost certainly stretch that cable.

How many here, would even know if a cable has been stretched or not?? As i say, cable pulling is an art, especially over long distances, were friction between duct and sheath play an important role!! Anyone can pull any size of cable into a duct with enough brute force, what the condition of that cable will be at the end of the operation is a whole different matter!!
 
thanks jd6400 a bit of sense at last , how on earth do these other people get work done i dont know , its a 16mm swa!!!! p.s i have pulled in more swas than most people on here have had hot dinners
 
As much as I respect near on every point you raise on this forum ! I am afraid no matter how you put it , a couple of blokes "hand pulling" a suitably secured and fed cable of this size , can not stretch it. I have assume that they are just average Joes and not part of the worlds strongest man competition that is of course .
 
Oh yes the conduit is it's that "thin stuff" Engineer 54!

One other thing I didn't mention. Customer slung MDPE water pipe in the same trench!

What would 528.3 conclude about that? - Since the cable will be down there in 100% humidity anyhow, maybe not a practical problem, but that type of argument could apply to any situation where you'd apply 528.3 so is probably unsound..
 
When are you doing this Justin? My tension levels are rising, Its like reading a novel but the last page is missing! I have to know who the murderer is!!!
 
Ha Ha! I visited yesterday and told the Customer at the time that since I was very concerned about getting the cable in in the first place I would have to "Investigate and consider the options". - No dates and no commitment.

There is plenty of other more accessible "normal" work required on the property which would be a shame to loose out on by being too negative about the "big one". Maybe I quote time and materials with a estimated percentage likelihood for my success. Honesty is the way forward, and no one would be hiding anything here. - That way there is at least a get-out for plan B if it went to worms.
 
As much as I respect near on every point you raise on this forum ! I am afraid no matter how you put it , a couple of blokes "hand pulling" a suitably secured and fed cable of this size , can not stretch it. I have assume that they are just average Joes and not part of the worlds strongest man competition that is of course .



Sorry, but your statement above, now comes into question ''(let alone stretch that cable in my humble experience)''!! Just how strong do you think 16mm SWA cable is against a couple of labourers that would be jerking and god knows what else to pull that cable in over a 150 meters, what with the cable itself weighing in at around 150/160Kgs.... Believe me 16mm SWA can be stretched quite easily, as well as physically damaged by any form of unsupervised dead weight pulling!! This cable could possibly fly in with no problems at all, and i hope it does. The difficulty comes when there is a problem, and what is done to overcome that or those problems...


As for iamelectric's statement, You have probably not come anywhere close to being involved in pulling more SWA cables than most of the older guy's on this forum. For a start, this project alone, has several Kilometres (if not miles) of ducted and direct buried cables. That would be for both MV and LV SWA cable as well as god knows how many signaling. As i say any fool and his dog can pull cables through a ducted system, given enough brute force, but at what cost to the cable, is another matter?? The bottom line is ''you need to know what you're doing and know the limitations of the cable you're pulling!!
 
But there is a lot of quite hard steel in that cable, In my book that's damn strong stuff and hard to stretch, but I appreciate your answer. So (..just say) the cable stretched by a fraction of a percent, - given the margins of safety, (for example 120% for current handling built into the most common interpretations of BS7671), would that be a problem?
 
Oh yes the conduit is it's that "thin stuff" Engineer 54!

One other thing I didn't mention. Customer slung MDPE water pipe in the same trench!

What would 528.3 conclude about that? - Since the cable will be down there in 100% humidity anyhow, maybe not a practical problem, but that type of argument could apply to any situation where you'd apply 528.3 so is probably unsound..

Not exactly an ideal situation, but shouldn't be of that much concern if this a smallish water pipe and isn't under too much pressure. Here the main concern is physical damage to the cable, caused by pressure movement of the water pipe after a rupture/burst at say a coupling, or a thrust block failure etc,etc.
 
If a couple of labours can get enough purchase on a bit of rope to stretch that piece of armoured I will eat my hat !!! I am not talking about yanking the hell out of it , and assume a modicum of sense is being applied to the pull and the cable is correctly secured , having said that .
 
i would say the water pipe is a major problem as ur draw rope was prob pulled in with the pipe its more than likely wrapped round the pipe throughout the ducting if it is u will have no chance of pulling the swa thru
 
i would say the water pipe is a major problem as ur draw rope was prob pulled in with the pipe its more than likely wrapped round the pipe throughout the ducting if it is u will have no chance of pulling the swa thru

Same trench, not same ducting. Edit: At least that's what I assumed. Perhaps not. Daz
 
Last edited:

Reply to Pulling 16mm SWA through 150 M of conduit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
486
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
356
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
943
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
3K
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock