Discuss Pulling cutout fuses in the UK Electrical Forum area at ElectriciansForums.net

davesparks

-
Mentor
Esteemed
Arms
Reaction score
17,142
We see a lot of threads asking what to do about isolation for a CU replacement with lots of talk of the seal fairy and just getting on and pulling the fuse.
It gets me wondering whether you do the same outside of the domestic world?

Does the seal fairy visit the heavy duty (over 100A) cutouts as often in your experience?

And another related question, do DNO's replace larger cast iron cutouts as a rule the same way they do in domestic?
 
Having done the G39 course I'm now very wary of pulling a fuse in a domestic scenario even with the correct PPE.

Commercially we always arrange for MOCOPA accredited persons to do it as the customer gets paid for it anyway unless they are un-metered supplies such as street lighting etc. I'mm ore than happy to let someone else take the risk.

A lot of the bigger sites we work on have dedicated facilites maintenance teams who sort all this out anyway with many outages taking place out of hours so the supply is already dead when we get there in the morning.
 
We see a lot of threads asking what to do about isolation for a CU replacement with lots of talk of the seal fairy and just getting on and pulling the fuse.
It gets me wondering whether you do the same outside of the domestic world?

Does the seal fairy visit the heavy duty (over 100A) cutouts as often in your experience?

And another related question, do DNO's replace larger cast iron cutouts as a rule the same way they do in domestic?
On the cast iron cut out query, Clients in my experience have basically said that they can’t afford the down time in having one changed where the premises is 24hr occupied so they never get it replaced, now whether or not the DNO have insisted it’s changed as it’s their equipment , I don’t know.
 
On the cast iron cut out query, Clients in my experience have basically said that they can’t afford the down time in having one changed where the premises is 24hr occupied so they never get it replaced, now whether or not the DNO have insisted it’s changed as it’s their equipment , I don’t know.

I'm currently dealing with places which are still on lockdown, it's the ideal time to get this stuff sorted, but UKPN seem to be allergic to answering the phone.
 
You should never, ever pull the main fuse, unless its a matter of urgent life or death situation. During my training, my tutor showed us a video of a test facility, where they pulled the main fuse with a special machine and the carrier had an unseen crack in it, so as it was pulled, the machine's 'fingers' touched the exposed metal contacts and 'BANG', a massive arc of bright light and the mechanical 'fingers' where either blown off or fused together. Imagine what that would do to flesh?
 
Having done the G39 course I'm now very wary of pulling a fuse in a domestic scenario even with the correct PPE.

Even without a course I'm very wary of pulling fuses, as much as I like fuse distribution boards like the MEM EXEL for their electrical protection I don't like pulling the fuses out.

Using a plasma cutter helps you realise what even a tiny amount of current can actually do to a piece of steel.
 
I agree, inserting or removing fuses on load gives me the willies and I happen to have some PPE (not the full stuff, only good to something like 4 cal/cm2 for hat+visor and 12 for insulated gloves).

And that is before considering old decrepit cut-outs that want to crumble when touched!
 
Having done the G39 course I'm now very wary of pulling a fuse in a domestic scenario even with the correct PPE.

Commercially we always arrange for MOCOPA accredited persons to do it as the customer gets paid for it anyway unless they are un-metered supplies such as street lighting etc. I'mm ore than happy to let someone else take the risk.

A lot of the bigger sites we work on have dedicated facilites maintenance teams who sort all this out anyway with many outages taking place out of hours so the supply is already dead when we get there in the morning.
Can you expand a little please Strima with regards the outcomes of pulling a fuse that you saw in your course?
 
I generally dont automatically rule out pulling fuses, being commercial and industrial. Although anyone attempting it with bare hands and without eye and face protection is running the gauntlet....
I do remember a couple of EICRs i was doing and you could clearly see the exposed screws on the fuse carrier as the little bit of insulation was missing, grabbing that with bare hands would have been a day to remember. Oh that was a C1 and stopped the EICR in its tracks..
Another was an old fuseboard mounted high up with exposed busbars, broken carriers, bare lugs etc. Totally refused to even look at it as even to prove dead was a risk... lol
 
Can you expand a little please Strima with regards the outcomes of pulling a fuse that you saw in your course?
On some cutouts there's an issue with insulation creep where the line conductor insulation has shrunk back and there's only a small air gap between that and the neutral cores on the split concentric cable. Not noticeable until you disturb it and everything vaporises in your face. I'm led to believe this is as recent as early 2000's that this cable was used as the problem didn't arise for a few years.

That small length of cable produces a very large, hot & fast moving cloud.

Minimum PPE is suitable face-shield, double layered insulated gloves and flash proof coveralls.

Even after an arc fault has occurred there's still further risk due to auto-closing devices at the substation so it may well go bang again.

Also when working on the cutout all terminations should be checked for tightness same as we do within a DB.
 
I will pull them in a domestic house, if absolutely necessary. I have done my ERG39 course with Scottish power, all be it that was for street light cutouts but same risks I would imagine.
It’s just a non starter getting someone from the DNO to come and pull a fuse. Luckily most new builds now have isolators.
On non domestic boards I will rarely pull the fuse, although I did last week where the seals were missing, obviously no under load to change a TP board in a small commercial unit.
 
If you do it - I would not and I recommend you do not - then at least make the effort to wear the appropriate PPE. I have used this company to equip personnel who connect high energy density batteries for 20 odd off-grid solar applications because of the very high short circuit currents. There are many others.:

Electric Arc Flash Protection Clothing | Electricity Safety - https://www.thesafetysupplycompany.co.uk/c/4536001/1/electric-arc-flash-protection-clothing.html

And this company provides insulated tools which we use to work on the batteries, inverters and solar arrays - again there are others:

Leading Manufacturer Of Insulated Live Work Tools - https://www.boddingtons-electrical.com/

What does your professional insurance stipulate you do or do not as a skilled competent person? In the world I once worked, an industrial setting, this work had to be done by the site's Approved Person (LV) or AP(HV).
 
Hypothetically, you could pull a main fuse with no load whatsoever.
Domestic, that should be easy to trace tails to any downstream mainswitch and turn off.
Clamp meter to prove no current is flowing, then yank it out.

Depending on condition of fuseholder of course......

Tinkerbell doesn't need PPE
 
In a domestic you can just turn off the consumer unit at the main switch and then remove the cut out fuse without load...
I do carry insulated gauntlets to wear.
I have seen guys remove tails from electric meters while still live, which imo is more risky than pulling a cut out fuse...
 
The DNO folk seem to pull/insert fuses on load, but rather them than me!

As said above, at the very least make sure the load is off. Worst thing you can do on accidentally inserting a fuse carrier on high load is to brick yourself and try to pull it out.

Most of the time folk don't think too much about clothing unless facing a real threat needing PPE, and for that you get proper arc-flash tops/trousers/etc. But one thing you ought to do anyway all the time you are working with possibly live systems is to wear natural materials such as cotton - yes it will burn under serious heat, but it won't melt and stick to your skin which makes any injuries much worse. Those polyester high-vis tops are a BAD idea here!

I have no idea what the DNO use in the way of PPE as it is not my area of work. In my case I have this for general head/face protection and it has some arc-flash rating:

Most gloves for arc-flash are leather over a rubber insulating type, but you do get insulating gloves that have mechanical strength and arc-flash rating, mine are:
[automerge]1598293082[/automerge]
If you are getting overalls but don't need the full arc-flash rating that some jobs demand at the very least you can look at flame-retardant ones. Some are suitable for welding, etc, and go a long way to protecting you from small incidents, for example:

But of course if your job actually means PPE is needed then you should make damn sure the correct ratings of PPE are provided for you and they are looked after!
 
Last edited:
as much as I like fuse distribution boards like the MEM EXEL for their electrical protection I don't like pulling the fuses out.
I do miss the MEM boards with the red spot-finger shock fuses, so many have been replaced now. I don't miss the Kantark stuff so much, cool to look at but it's anyones guess if the old jammed in ceramic carrier will pull out without breaking.
 
Pulling fuses on any type of cutout, without the correct ppe is dangerous, the risk is even higher with industrial/commercial cutouts with j type fuses.
Please dont do it.!!
 
How bright is bright? Light can be measured in units known as lux, which is a measurement of illuminance and equal to 1 lumen per square meter. To put it into perspective, a typical overcast day is about 1,000 lux. Direct sunlight is upwards of 100,000 lux. The light intensity of an arc flash 3 meters from the source is over 1 million lux, and a more recent arc flash test recorded 13.1 million lux—approximately 130 times brighter than direct sunlight! Read that, now that’s bright
 
The usual arc-flash threshold for PPE being necessary is 5 cal/cm2 as that is the onset of 3rd degree burns (i.e. not going to heal to as-before EVER).

To put that in to perspective, 1 cal/cm2 is roughly equivalent to holding a lighter on your skin for 1 sec!
 
Of course a sensible Government or Governing Body would have ensured by now that the smart meters being rolled out included an isolator, as some used to I believe.

Instead we have this situation where everyone knows what happens, but nods and winks and won't ever either ban it or put it in writing where it can be done.

I was told of a mythical scheme where certain competent persons could be trained and issued their own temporary fuse seals, which would be used when replacing the fuse - and then replaced when the DNO came along to check and replace with theirs. However, UKPN had never heard of it when I approached them, and were unable to give me any good advice on how to do things 'correctly' other than to point at the regulations.
 
Was watching NPG install a replacement 400A fuse at his sub and he used a device which plugged into the fuse carrier to make sure there was no or low load before inserting the fuse proper. Dont know what it was but it looked a bit technical to be nothing more than continuity tester.
He also wore full head gear , face shield and apron
 
I have seen (product description, not first-hand) a fuse carrier for the 400A sort of range that allows remote connection of the fuse for safety, and to have two fuses so it can auto-reclose once to reduce fault outage time.

Forget where I saw it, alas :(
 
How about pulling BS3036 fuses. Does everyone always switch off the main switch of the CU before pulling one of these fuses as you'll never be able to make sure you are not pulling the fuse under load otherwise?
 
I am definitely of the school of don't touch the cut-out/DNO/metering equipment. I think we all know the dangers if something goes wrong and boy does it ever go wrong when it does. It's not just the cut-out that presents a danger but also the cable and its' state which may short out if manipulated via the cut-out.
Having said that...I had a new three phase cut-out replaced by the DNO and they left. As the smart HH meter had been disconnected, even though they reconnected there was no live out of the meter. Phoned them and they re-attended. They took out the fuse and tested as I would not, and said why didn't I take out the fuse. I said it's illegal to which they tsked tsked and gave knowing looks and suggested it would have been ok for me to do that. So go figure!
I would definitely no way touch anything above domestic 100a, instinct alone forbids it.
 
I think it’s Haste. I tried calling them to do an isolator but they didn’t cover my area which is SSE.
I've been meaning to contact them since I saw it in one of his videos so emailed them last night, but apparently they don't offer that service any more and just suggested I contacted my local distributor :rolleyes:
 
It's a funny one around here as I literally straddle 2 dnos. I just moved out of Bath to Peasedown. western power say don't pull fuses at all yet SSE say if you are in a scheme and it's a single phase upto 100a domestic only property you can pull fuse they will even give you seals to put back on afterwards. If fuse looks old or damaged give them a call.
 
With an HRC such as a BS1361, closing onto a fault should cause a rupture within the cartridge and hopefully no arc outside of it. Therefore the greater risk is drawing an arc at the carrier contacts by pulling it under load and more so under fault conditions. I like to position it ready and then push it home into contact with a closed hand so that if anything goes wrong and I recoil, I won't take the fuse back out unintentionally. To pull it under (normal) load is a matter of being very swift and certain, assuming the design is not prone to arcing over to the casing etc.

How about pulling BS3036 fuses.

With a rewirable (and there were rewirables before BS3036) there is also the risk of an arc in free air if the fuse ruptures when closing onto a fault, or if a fault occurs when the covers are off. There are some traps for the unwary, e.g. on a metalclad Wylex, a plasma bridge can form between the bottom (unfused) terminal and the edge of the aperture in the front panel which would normally be intercepted by the lip on the plastic cover. With a professional hat on, I would therefore never choose to handle these fuses live.

With my historical hat on, I might have been seen to insert channel fuses on a live circuit. That's the type where the fuse wire lies along an open channel facing the user and comes flying out at you when it ruptures. Needless to say, these things were invented when typical fault currents were very much lower than they are today.
 
With my historical hat on, I might have been seen to insert channel fuses on a live circuit. That's the type where the fuse wire lies along an open channel facing the user and comes flying out at you when it ruptures. Needless to say, these things were invented when typical fault currents were very much lower than they are today.
Here is some photo of a glass fronted fuse box with those fuses, I don't know where this was removed from:
fuse.jpg
fuse2.jpg
fuse3.jpg
 
personally I prefer to pull the tails out of meter live. less chance of any problems with a cut'out fuse. (obviously after ensuring that there is no load on the installation). L out first, then N. N in first, then L.

( substitute "I" for "a spark that I know")
 
personally I prefer to pull the tails out of meter live. less chance of any problems with a cut'out fuse. (obviously after ensuring that there is no load on the installation). L out first, then N. N in first, then L.

( substitute "I" for "a spark that I know")
The least-worst option if the cut-out is old and dodgy and it simple has to be done then.
[automerge]1600590429[/automerge]
But obviously not something any of us would ever recommend...
[automerge]1600590570[/automerge]
Here is some photo of a glass fronted fuse box with those fuses, I don't know where this was removed from:
I have seen photos of other Tucker Telac fuseboxes and they are works of art really. Just not something you would want to encounter live these days!
 
That box is nice, Freddo, because it's an 8-way. Many 2 / 3/ 4 way boxes survived because they were used in so many homes, but 8-way are rare and its great that this one has been saved.
 
I recently was called out to look at a possible rewiring job, The customer had someone in to do some work in the bathroom (6 months prior) as part of that work they changed to consumer unit and put an Earth stake in.
Anyway the consumer unit was a mess, you could tell the previous electrician didn't quite know how to fit a new mantel unit and as a result he got himself in a bit of bother...
I'm not quite sure of the series of events but I was curious to why the previous electrician had put a rod in, I could see it would have been an TNS supply, I also noticed that I could see evidence of superglue around the rear of the cutout....
Its not obvious but when you look carefully at the picture you can see the whole cutout has dropped and its not fixed.
It was then I noticed scorch marks on the bottom of the mantel unit...
I believe the previous electrician pulled the fuse and shorted the incomer to the mantel unit, possibly losing the suppliers earth at the same time...

Fortunately I noticed this as if I had just gone in and pulled the main fuse I would have been in serious trouble, but this has definitely changed my view on pulling main fuses.


20200121_101319.jpg
20200825_085438.jpg
20200825_085741.jpg

[automerge]1600596371[/automerge]
Pictures of afterwards to save the customer costs I re-used the old unit, I know its not the neatest.
The DNO came after I'd finished so when I csme back to connect the suppliers earth up so I left the 100ma Upfront RCD in.
20200903_084902.jpg
 

Attachments

  • 20200903_090006.jpg
    95.8 KB · Views: 22
Last edited:
Fortunately I noticed this as if I had just gone in and pulled the main fuse I would have been in serious trouble, but this has definitely changed my view on pulling main fuses.
Yes, a lucky escape there. As you say, something to be very cautious about doing.
Pictures of afterwards to save the customer costs I re-used the old unit, I know its not the neatest.
It is still a huge improvement!
The DNO came after I'd finished so when I csme back to connect the suppliers earth up so I left the 100ma Upfront RCD in.
No harm in that.
 
as above, a huge improvement, even though it'd protecrap.
 
That box is nice, Freddo, because it's an 8-way. Many 2 / 3/ 4 way boxes survived because they were used in so many homes, but 8-way are rare and its great that this one has been saved.
It's a shame many of the fuse carriers are crumbling apart, this one has been on the shelf in the office of my now retired boss. It was moved out of there the other day, I will ensure it doesn't head towards the skip.
I know its not the neatest.
It's a massive improvement, looks great! :thumbsup:

That before photo is absolutely farking disgusting, there is no excuse for anyone to be carrying out work to such a poor standard.
 

Reply to Pulling cutout fuses in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
1K
Objective: allow fast charging of EV (22 KW) DNO cutout has 3 100A fuses, but all 3 turned out to be on the same single phase How to still obtain...
Replies
3
Views
909
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock