it's not going to trip a RCD. only take it out of service if it's not a critical component.whilst awaiting replacement. might be an idea to check for any water ingress to terminals etc.
 
so leave in service pending further investigation or replacement.
 
What size motor? Squirrel cage? Submersible? Outdoors? Cold & damp?

On some motors I would be delighted to get nearly a megohm and would be quite happy to leave in service. Others I would expect better.
 
possible that the IP68 rating has started to break down.
 
Sounds OK to me for a used pump. There are many variables with a submersible, including the length and type of cable submerged, that make a single insulation resistance reading a rather imprecise indicator of motor condition. What is more important is how that reading varies with time. If you come back in 3 months and find it at 600kΩ, and then at 300kΩ, you can see something is deteriorating. But if it stays around 900kΩ it's probably fine.

There's a good summary here:
YCC Pump insulation test recommendations

I've just read that and the paragraph about cable capacitance charging up is not strictly correct, they are confusing capacitor charging and dielectric absorption. The cable does have capacitance, and the capacitance to earth is increased by the cable being submerged in earthed water. The capacitance does have to charge up when the IR test is first applied but this will typically happen within seconds (the time constant is the product of the dynamic source resistance of the tester's voltage source and the capacitance) What then happens over a longer period of test voltage application is the dielectric absorption effect. This involves a smaller current than the charging current and it is limited by the properties of the insulation. It can influence the resistance indication on the tester so there is value in waiting for the numbers to stop increasing.
 
Last edited:

Reply to Pump under 1megohm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Sorry if this is a stupid question. We have a waste water pump in our first floor flat. The water pump failed and stopped draining water from the...
Replies
4
Views
274
Hello. How i should connect this 1 phase 2 pole 400v cooling pump? If i apply 1phase 230v and neutral it Will only growl and "spin" very very...
Replies
11
Views
732
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off...
Replies
2
Views
782
Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Replies
17
Views
689
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock