Is it the pump or the pump supply wiring that's giving you this reading?If a pump is below 1mega ohm should it be condemned? Pumps reading about 0.9meg? Thank you for your replies
The pump itselfIs it the pump or the pump supply wiring that's giving you this reading
If you can't see any obvious damage /problems, send it away for repairs or source a replacementThe pump itself
We’re awaiting replacement my question is should it be condemned until we have the replacement?If you can't see any obvious damage /problems, send it away for repairs or source a replacement
It’s crucial yeah but no rcd on the circuit fed from BS88 2 16 amp fusesit's not going to trip a RCD. only take it out of service if it's not a critical component.whilst awaiting replacement. might be an idea to check for any water ingress to terminals etc.
It’s a 2.2kw submersible pump?What size motor? Squirrel cage? Submersible? Outdoors? Cold & damp?
On some motors I would be delighted to get nearly a megohm and would be quite happy to leave in service. Others I would expect better.