piz

Hello all,
I have been to a property with a crabtree starbreaker board main switch is 80A 30ma rcd.
The customer thought the dishwasher was tripping electrics I teste IR when I tested RCD it tripped on times half!
I have ordered a new one but when the breaker is turned off for the PV the rcd no longer trips, Would this be a PV fault been insalled over a year can we test them? (PV)
wht would it trip if only feeding?
Cheers
 
You may have got a better response posting in the solar photovoltaic forum rather than tools and products.

PV generates stray DC voltage on the AC side and can trip an RCD very readily. This is not a fault, it is characteristic of PV.
Normally PV is installed in such a way that it is not required to have an RCD on the circuit.
Check the installation method and see if the PV can be relocated on a non RCD circuit.
 
Whoever installed the PV system on a board protected by a single RCD has created a dangerous situation.
Many, if not all of the circuits protected by the RCD would be required to disconnect within 0.4s. A PV inverter can take up to 5s to shutdown which means than circuits could remain energised via the inverter for longer than their 0.4s maximum when the RCD trips.
I suggest that the PV system is removed from the upfront RCD protected CU, a separate 2 way CU is installed via henley blocks in the main tails and the PV is fed from that.
 

Reply to Pv tripping rcd in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
793
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock