Discuss Question regarding filling Section K of Electrical Installation Condition Report. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nazoom

Hi

I am trying to fill in Section (K) of Electrical Installation Condition Report. My question is when we have faults like: High Insulation resistance on a certain circuit that i know, High resistance of main bonding that i identified, Zs too high for ring, ring discontinuous and incorrect polarity for light circuits that i inspected. What do i put in the (Furhter Investigation Required) section? For these faults do i put No or Yes?

Many Thanks
 
You will have listed faults and defects in section F. In the tick box section of items inspected if a code is attributed to a particular item I refer it to section F. ie....'Section F item 3'.
The FI box would only be used if you were unable to reach a conclusion about an item and further investigation is required...again this could be referred to section F. In practice the FI box is almost never used as in most cases if you have coded an item no FI is needed,just rectification.
 

Reply to Question regarding filling Section K of Electrical Installation Condition Report. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
happysteve submitted a new resource: EICR - Electrical Installation Condition Report - BS7671 2018 + A2:2022 - Fillable EICR PDF form for 18th...
Replies
12
Views
3K
Hey guys - I am in the process of buying a flat, and just got the electrical installation report. Seeking for feedback on the following: - THE...
Replies
17
Views
4K
I was surfing through one of the electrical training groups on Facebook yesterday and came across this question from an AM2 prep course: There...
Replies
7
Views
997

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock