could always test with your wander lead, the resistance of which you should know ( typically 0.3 - 0.5 ohms), then deduct similar to previous suggestions.
 
I was always taught not record a 'measurement' of zero, mark it up as 0.01.

It's more satisfying to see a plausible-looking number but may be technically less correct. It depends whether whoever is reading the results understands measurements properly. If you give the precision, or it's apparent from the number of digits, you are not claiming that the resistance is actually zero, but that it lies in a range that is numerically displayed as zero on the instrument.

R=0.0Ω means R lies between -0.05Ω and +0.049Ω, +/- any of the normal sources of error: Instrument offset, scaling error, display precision error and reading error.
R=0.00Ω means between -0.005Ω and +0.0049Ω likewise.
For passive circuits obviously the negative part of the range is not applicable.

In engineering and scientific work, one must always record what the instrument displays. That way, the results should be reproducible by someone else with the same instrument. If you make it up, you can't backtrack in the light of some later discovery (e.g. that the instrument always reads 0.02Ω low) or that some assumption you made was valid, because the original information (that the display said 0.0Ω) is lost.

With MFTs and low resistance cables, I agree that a common source of error is making better contact during the test than during cable nulling, in which case the computed reading will be low by the amount that the stored null offset is high.
 
You cannot record zero on the cert as this would be incorrect, the cable is 8m long there must be some measurement of resistance there.
If your testers calibrated and functioning as designed then you enter the result it gives you, anything else is a fabricated number.
 
0.18 same as Ze,(tncs) i hit test 3 times when doing Ze and it was always the 0.18 mark (slightly lower but the 0.18 was the highest reading) Zs was probs straight onto bare cable after terminating into back of cooker (I would normally be happy to calculate Zs on a single radial like that but did the test anyway due to the low R1+R2) i installed new 2 way Cu after splitting the tails through a new henly block,new tails (25mm) new 16mm earth and new 10mm (IR >2000) as before no more than 8 mtrs from cooker to new cu (in trunking whole route) 100a main switch and 40a rcbo (rcbo tested fine 32.6 ms x 1 and 29 ms x 5) as per previous post I wasn’t willing to install new circuit in existing Cu due to state it was in,newish board (not to 17th Editon) but clearly not fitted by anyone with any experience of electrical works in any capacity ever,
 
Giving it some thought, if I’d gone with the lowest Ze of 0.16 and then did Zs and got 0.18 I’d have been happy but that still wouldn’t explain the 0 R1+R2 result? Or am I missing something?
 
Giving it some thought, if I’d gone with the lowest Ze of 0.16 and then did Zs and got 0.18 I’d have been happy but that still wouldn’t explain the 0 R1+R2 result? Or am I missing something?
See post 56
 

Reply to R1+R2 of zero zilch nothing?...... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock