Discuss Range Oven Tripping Circuit Breakers in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
We just had a range oven fitted (gas on hob with two electric ovens - total power rated at 5.3Kw) so a 32Amp mcb is in the board on the dedicated cooker circuit which was there from previous cooker. When one oven is on everything works fine, but when both ovens are switched on together they trip the main 63Amp breaker in the consumer unit before the 32Amp mcb trips. It seems odd that both ovens work perfectly when on individually, but the minute you switch both on together they trip the main 63 Amp breaker in the consumer unit - this has been tested with everything else in the house switched off for all intents and purposes so there is nothing else bar the odd light and fridge still on - so no kettles, immersion heaters etc... Both ovens work great individually and nothing trips circuit breaker wise, but the minute they are both on together they trip out the entire consumer unit - the consumer unit is a 10 way split load and less than a year old so my thinking is a fault with the oven wiring and maybe a loose connection inside it as the oven is a second hand reconditioned one and not new from a store. Has anyone seen this fault before or maybe have an idea what the problem may be - bearing in mind both ovens do work individually? Thank you in advance
 
i'll make an educated guess that that 63A device is an RCD. and there is sufficient earth leakage either in the ovens, or with the ovens combined with other devices, to trip it. does ithave a test button on it, like this:

77px-Residual_current_device_2pole.jpg
 
My partner says she is not bothered about only using one oven as she would only ever use two on Xmas day (wish I had known this before this big range was bought!!!) and says it's no big deal if she only had one oven on that day too, so she doesn't care - however, I would just like to see what the problem may be and see if I can resolve it.
 
then it tripping through earth leakage. could be damp in the oven elements, or a combination of small faults adding up to breach the 30mA threshold of the RCD. afraid you will need a competent electrician with the relevant test gear to sort this one. but first, i'd switch each oven element on, one at a time and allow each to run hot for a while, then switch 1stone off and do same with 2nd, etc. then try them all together.

bear in mind that a RCD does not trip on overload or short circuit, so those 2 can be dismissed as causes.
 
Both ovens work great individually, but when both are on they trip the RCD - however the fact this is reconditioned with new elements in it and it has stood in a damp house (being done up) for nearly eight months. So I will switch each oven on individually for an hour and see if it helps (thanks telectrixs). After that I will take a look at the earth connections in the board and at cooker switch and see if something may be a little loose - might be in the cooker as the cable looks brand new so someone will have done that when reconditioning it...
 
We just had a range oven fitted (gas on hob with two electric ovens - total power rated at 5.3Kw) so a 32Amp mcb is in the board on the dedicated cooker circuit which was there from previous cooker. When one oven is on everything works fine, but when both ovens are switched on together they trip the main 63Amp breaker in the consumer unit before the 32Amp mcb trips. It seems odd that both ovens work perfectly when on individually, but the minute you switch both on together they trip the main 63 Amp breaker in the consumer unit - this has been tested with everything else in the house switched off for all intents and purposes so there is nothing else bar the odd light and fridge still on - so no kettles, immersion heaters etc... Both ovens work great individually and nothing trips circuit breaker wise, but the minute they are both on together they trip out the entire consumer unit - the consumer unit is a 10 way split load and less than a year old so my thinking is a fault with the oven wiring and maybe a loose connection inside it as the oven is a second hand reconditioned one and not new from a store. Has anyone seen this fault before or maybe have an idea what the problem may be - bearing in mind both ovens do work individually? Thank you in advance
The "63 Amp breaker" you talk of that would an RCD wouldn't it? which I think indicate an earth fault on one of the ovens
 
You have tried using the ovens with everything else switched off
Have you tried disconnecting as many of these items as possible,unplugging rather than switching off
It will disconnect the neutrals and remove a low neutral-earth on another circuit that may be playing a part
 

Reply to Range Oven Tripping Circuit Breakers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
721
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
800
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock