Hi,

Anyone have experience in the following:

16a MK RCBO Tripped supplying Garage. 2 Circuits. Radial and Lights (6/16) MCB's

PME supply. Garage supplied in 6mm Twin and Earth with the Earth connected at the Main DB and Connector Blocked in the garage (doing nothing). Earth rod to garage in 6mm Multistrand and connected.

Twin and Earth IR Line/Neu +999, Neu/Earth +999 and Line/Earth 0.01. Removed Earth from main Cu and RCBO stable and live.

Zs 46.6 using just the Earth Rod, connected at the sub board in the garage. RCBO test sequence all clear too. Plugged in Freezer and RCBO tripped. Re-set RCBO and the Freezer is now stable.

2 Questions

Do you connect the CPC on the T/E at the MAIN Db when using RCBO's to supply a garage PME supply?
Any ideas why the freezer tripped the RCBO initially when plugged in for the first time? Leakage currents? RCBO ramp test was 21.0mA

Cheers
 
Last edited:
might have tripped on the MCB part due to inrush current. might be an idea to replace with a type C.
 
PME supply. Garage supplied in 6mm Twin and Earth with the Earth connected at the Main DB and Connector Blocked in the garage (doing nothing). Earth rod to garage in 6mm Multistrand and connected.
The begging question why is the earth connected to the earth at the main board
And its a TT in the garage Is their any water pipes in the garage?
 
The CPC for the distribution circuit should be connected to earth at source.

How old is this freezer? Could be its just getting old and drawing too much current on start up. A standard domestic freezer should work quite happily on a B curve MCB.
 
Twin and Earth IR Line/Neu +999, Neu/Earth +999 and Line/Earth 0.01. Removed Earth from main Cu and RCBO stable and live.

Is that statement correct?

If the freezer hadn't been plugged in for a while it may have a fault on it when the compressor is cold and now powered it's gone.
However it may return if it's ever turned off or it gets cold in the garage.
 
Hi,

Anyone have experience in the following:

16a MK RCBO Tripped supplying Garage. 2 Circuits. Radial and Lights (6/16) MCB's

PME supply. Garage supplied in 6mm Twin and Earth with the Earth connected at the Main DB and Connector Blocked in the garage (doing nothing). Earth rod to garage in 6mm Multistrand and connected.

Twin and Earth IR Line/Neu +999, Neu/Earth +999 and Line/Earth 0.01. Removed Earth from main Cu and RCBO stable and live.

Zs 46.6 using just the Earth Rod, connected at the sub board in the garage. RCBO test sequence all clear too. Plugged in Freezer and RCBO tripped. Re-set RCBO and the Freezer is now stable.

2 Questions

Do you connect the CPC on the T/E at the MAIN Db when using RCBO's to supply a garage PME supply?
Any ideas why the freezer tripped the RCBO initially when plugged in for the first time? Leakage currents? RCBO ramp test was 21.0mA

Cheers
Is the garage separated from the house? If so hopefully the T&E is run in some form of conduit? I assume there was a reason originally for them not to want to export the PME - Metal structure? Pipes?

The earth would be connected at the MAIN db to protect the cable (as armour would be if it was SWA) . If the L-E reading was 0.01 on the T&E with it disconnected at both ends then there is damage to the cable which would need to be found.
 

Reply to RCBO Fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock