Maximum Zs values for Type 4 devices have never been quoted in the Regulations so you have to refer to manufacturers figures. Type 4 devices unlike other circuit breakers used 0.4 and 5 sec disconnection times, so 0.4 for socket outlets and 5 sec for fixed equipment.
 
It may get to a point that if any further additions/work is carried out and requires RCD/RCBO protection a new consumer unit would be cheaper in the long run if the prices are too high eg a BG 5 +5 split £73 inc VAT.
 
Replacement is another option, but it would a fair job, as there are also off-peak circuits so would require two new consumer units.

Square_D_QO1_12F_DB_2.jpg
 
I cant see how **** arsing around putting an rcd inline below the board is gonna work out cheaper than the £65.28 that a correct new rcbo is?

That is probably true. They won't grudge spending the money, I told them something should be done before any alterations are made.

I will just buy one.

Thank you all for helping me bat some ideas around and pointing me to a suitable retrofit item.
 
I replaced the circuit breaker with the new RCBO last night.
I tested the circuit Riso, Zs, and the RCD trip times.

Riso live conductors to earth was under 1 Mohm so needs some further investigation, but not at 8.30 in the evening.
Zs 0.77 ohms.

The RCD trip times are not meeting the requirements for additional protection.

I repeated the test three times using a Fluke MFT, the meter was set for the correct characteristics - type AC, 30 mA.

x1 - 49.4 ms and 76.5 ms - less than 300 ms so acceptable.
x5 - 41.6 ms (180 deg.) and greater than 50 ms (0 deg.) - neither are acceptable readings for providing additional protection as over 40 ms.

A quick Internet search did not reveal what the operating times should be for the BS EN 61009-1 product standard (if any different to those quoted to meet the requirements in BS 7671).

I am considering contacting the supplier to ask about a replacement RCBO as I am not entirely happy with it, but I first I wanted to try and find out whether the product is working as it should or not, hence the question about the product standard requirements versus BS 7671.
 
Last edited:

Reply to RCBO for old Square D distribution board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
873
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
770
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
786
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
868

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock