I replaced the circuit breaker with the new RCBO last night.
I tested the circuit Riso, Zs, and the RCD trip times.
Riso live conductors to earth was under 1 Mohm so needs some further investigation, but not at 8.30 in the evening.
Zs 0.77 ohms.
The RCD trip times are not meeting the requirements for additional protection.
I repeated the test three times using a Fluke MFT, the meter was set for the correct characteristics - type AC, 30 mA.
x1 - 49.4 ms and 76.5 ms - less than 300 ms so acceptable.
x5 - 41.6 ms (180 deg.) and greater than 50 ms (0 deg.) - neither are acceptable readings for providing additional protection as over 40 ms.
A quick Internet search did not reveal what the operating times should be for the BS EN 61009-1 product standard (if any different to those quoted to meet the requirements in BS 7671).
I am considering contacting the supplier to ask about a replacement RCBO as I am not entirely happy with it, but I first I wanted to try and find out whether the product is working as it should or not, hence the question about the product standard requirements versus BS 7671.