Would you deem a socket (twin or commando) to be exempt from requiring RCD protection if it is fitted above a suspended ceiling installed to supply a specific piece of equipment?

Initially I'm thinking yes. Wouldn't think anyone is going to go out of their way to access them if there are other sockets dotted around at standard height.

Thoughts, please?
 
The regulations (411.3.3) require an RCD for all socket outlets with a rated current not exceeding 32 amps, unless a documented risk assessment is carried out, explaining why an RCD is not required.
Except for a socket outlet in a domestic installation, which cannot be omitted for any reason.
 
Would you deem a socket (twin or commando) to be exempt from requiring RCD protection if it is fitted above a suspended ceiling installed to supply a specific piece of equipment?

Initially I'm thinking yes. Wouldn't think anyone is going to go out of their way to access them if there are other sockets dotted around at standard height.

Thoughts, please?
If it’s non-domestic the yes, you can do a risk assessment and omit RCD’s if that determines one is not required. See 411.3.3.

If it’s domestic there is no exception unless the cables are surface mounted and visible along their length, and even then that has caveats.
 
If it’s non-domestic the yes, you can do a risk assessment and omit RCD’s if that determines one is not required. See 411.3.3.

If it’s domestic there is no exception unless the cables are surface mounted and visible along their length, and even then that has caveats.
Yeah, I've never understood that as cables on show I prefer to provide with RCD protection just as a bit more protection incase they get damaged.
 
Yeah, I've never understood that as cables on show I prefer to provide with RCD protection just as a bit more protection incase they get damaged.
Agreed, its a sentence in the OSG that doesn’t make much sense to me either.

The paragraph above it (3.6.1 (b)) and 411.3.3, are clear that RCD’s are required for sockets outlets. Then you‘re told (3.6.2.1) they’re not specifically required for surface mounted cables.

Like you I’d fit them anyway.
 
Why would you NOT want to fit a RCD?
  • Critical loads that you don't want spurious trips on.
  • Stuff with very high leakage current (e.g. supply to rack of computers where you want to be able to change the UPS without getting a sparky in).
  • Stuff with nasty waveforms that might trip one (e.g. some older high-power welders).
  • Where it is not really required for safety and would require a board change or other means to actually implement it.
Those are unusual cases, but they do exist outside of domestic situations.

Even for domestic, putting spoke alarms on a MCB would be preferable to a RCBO. Or on the lights circuit as then the loss of power is noticed if it trips one day due to external influences (e.g. lightning surges or other high dv/dt effects from faults).
 
Last edited:

Reply to RCBO required? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
690
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I live in a property built in 1911. It has had asbestos artex applied to every ceiling in the house. I am currently creating a new...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock