Discuss RCBO tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
76
Anyone an idea why an RCBO measures >40ms on a 5x test on the second half of the sine wave but all other tests are within requirements? Sorry, it's not a single RCBO, there's 2 RCBOs in this board and both have similar results leading me to think not a faulty RCBO but an issue further upstream somewhere. Continuity, IR, Zs all textbook.

Trip times are something like 48ms on 1x, 28ms 5x on first half and >40ms second half 5 for both devices. No other RCBOs in the board but a different, adjacent board's RCBO tests fine.
 
Nothing for certain but a technical thought ,since DC
sensitive RCBO's have been mentioned !
Are there any DC powered appliances - PC Power supplies,inverter washing machines present.
(Wacky idea, each half cycle has a polarity , Are we looking at a pulsed DC leak de sensitizing 1 polarity ?)...
I may just be a rabied dog barking up a theoretic tree ... Faults do come in batches .
(though does feel like a feature of install / or test gear brand mix)
-----
rolyberkin was having similar problems with a 32A
Lewden.
RCBO Test data - 40 milliseconds
I Have my doubts at times with MFT
software -"recognising test results" that are not common yet !
 
With the pods the manufacturer advises that You have to remove the wire from the terminal and just insert the probe into the terminal.
The only probe I’ve managed to inert are the very fine ones that screw or insert onto the tests lead

Unsure if this is 100% correct
 
Last edited:

Reply to RCBO tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
Last week I took the opportunity of having the mains power off to test the RCBOs in a Wylex Consumer Unit, fitted nearly 5 years ago, which has...
Replies
2
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
887

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock