Discuss RCBO tripping on outside lights in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
21
Hi all,

Wondering if you could offer some advice please.
I carried out a small outdoor lighting project today at a commercial property. 4 lights controlled by a photocell.

As a background, the cables were installed by the resident electricians. 1.5 SWA at all 4 lights. The supply is ran back to a 10amp C type mcb near the main building.

Site management requested that the lights have a timer and photocell on them, which gives them a couple of options going forward. So in a large JB, I brought the supply cable to a 6A rcbo, onto the timer, from timer on to photocell, from photocell to a contactor, which brings on lights when pulled in by photocell.

However, when I powered up, the 6A rcbo tripped. After checking wiring was OK, I chanced replacing the rcbo for an mcb just to see. And it didn't trip. So I'm assuming it's a neutral issue, as all neutrals were common.

Can anyone shed some light on what might have caused this?

Thanks all
 
If you have interconnected the neutral conductors between the lighting and control circuits an RCBO it is bound to trip. Aside from these circuits needing separation as you have created a dangerous situation does it actually need an RCBO.
 
If you have interconnected the neutral conductors between the lighting and control circuits an RCBO it is bound to trip. Aside from these circuits needing separation as you have created a dangerous situation does it actually need an RCBO.
Thanks for the response.

I'd be more of a domestic sparks but I'm now picking up more work in commercial sector. So from that I did understand, to an extent, that this separation was needed. In my own head I wanted to offer more protection to the circuit by using an rcbo, ie O/Load and S/Circuit protection. And isn't always a good idea to have some form of rcd protection on certain external installs?

Just to add, the mcb feeding our control box was a 20A. So that had RCD protection of its own. Is it correct for me to assume I crossed the neutrals given that the 20A was coming off an rcd neutral bar?
 
I'll avoid RCD protection unless it is absolutely required for additional or fault protection.
Not really understanding your last sentence.
 
Hi all,

Wondering if you could offer some advice please.
I carried out a small outdoor lighting project today at a commercial property. 4 lights controlled by a photocell.

As a background, the cables were installed by the resident electricians. 1.5 SWA at all 4 lights. The supply is ran back to a 10amp C type mcb near the main building.

Site management requested that the lights have a timer and photocell on them, which gives them a couple of options going forward. So in a large JB, I brought the supply cable to a 6A rcbo, onto the timer, from timer on to photocell, from photocell to a contactor, which brings on lights when pulled in by photocell.

However, when I powered up, the 6A rcbo tripped. After checking wiring was OK, I chanced replacing the rcbo for an mcb just to see. And it didn't trip. So I'm assuming it's a neutral issue, as all neutrals were common.

Can anyone shed some light on what might have caused this?

Thanks all
Did you test all lights individually before installing them? One of them might be the problem. Kind regards, Kevin
 

Reply to RCBO tripping on outside lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
767
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock