Discuss Rcbo's in the Industrial Electricians' Talk area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Just finished installing power sockets in It suites at a school.
All protected by 30 ma rcbo's ,circuits specified by electrical consultants,15 2 gang skts on each circuit.All working & no trip outs.
My reckoning was about 7 2 gang skts per circuit,what's your feelings on this.
Have I gotta change my reasoning on these circuits & follow suit.
 
A good idea would be to measure the actual earth leakage on the circuits with all sockets in use. I would be interested to know the results.

I used to do a lot of IT room installs for a previous company and the local authority spec was 6 double sockets per 32A ring circuit. This was based on one workstation (one pc and one monitor) per double outlet. I always thought this was a bit on the cautious side.
 
Depending on the size of board and number of circuits you can find yourself fast running out of earth terminals.
.... And it throws them out of sync when every other terminal is in the correct termination number wise.
 
Last edited:
Depending on the size of board and number of circuits you can find yourself fast running out of earth terminals.
.... And it throws them out of sync when every other terminal is in the correct termination number wise.
Not a problem using 18 way TPN DB,all earths connected correctly for installation
 
Depending on the size of board and number of circuits you can find yourself fast running out of earth terminals.
.... And it throws them out of sync when every other terminal is in the correct termination number wise.

Carp just take your time jobs a good un, two earth terminals at the DB for either a Ring or Radial final circuit nothing difficult or out of the ordinary for a good Sparky, although it doesn't apply to the Domestic Installers.
 
Not a problem using 18 way TPN DB,all earths connected correctly for installation
I recently did a small(ish) office which had amongst other things 3 radial cct's with high integrity earthing fed from a 10 way single phase board. I installed an extra earth bar to accommodate the extra cpc's but didn't use it in the end as I found a different way of doing it and still achieve compliance with the regs.
 
I think this is where the Regs trips it self up in situations like this, apart from a few additional terminals for main earths, bonding etc, no standard DB can fulfill the requirements for high integratity earthing comprising more than a couple of circuits and unless the additional earth conductors are cable I'd, it would make it very confusing for the next person coming along at a later date.
 

Reply to Rcbo's in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
774
Hi there, I am looking for some advice re: putting new sockets and usb sockets in my home. Someone will be rewiring the entire house but I have...
Replies
19
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock