Just finished installing power sockets in It suites at a school.
All protected by 30 ma rcbo's ,circuits specified by electrical consultants,15 2 gang skts on each circuit.All working & no trip outs.
My reckoning was about 7 2 gang skts per circuit,what's your feelings on this.
Have I gotta change my reasoning on these circuits & follow suit.
 
A good idea would be to measure the actual earth leakage on the circuits with all sockets in use. I would be interested to know the results.

I used to do a lot of IT room installs for a previous company and the local authority spec was 6 double sockets per 32A ring circuit. This was based on one workstation (one pc and one monitor) per double outlet. I always thought this was a bit on the cautious side.
 
Depending on the size of board and number of circuits you can find yourself fast running out of earth terminals.
.... And it throws them out of sync when every other terminal is in the correct termination number wise.
 
Last edited:
Depending on the size of board and number of circuits you can find yourself fast running out of earth terminals.
.... And it throws them out of sync when every other terminal is in the correct termination number wise.
Not a problem using 18 way TPN DB,all earths connected correctly for installation
 
Depending on the size of board and number of circuits you can find yourself fast running out of earth terminals.
.... And it throws them out of sync when every other terminal is in the correct termination number wise.

Carp just take your time jobs a good un, two earth terminals at the DB for either a Ring or Radial final circuit nothing difficult or out of the ordinary for a good Sparky, although it doesn't apply to the Domestic Installers.
 
Not a problem using 18 way TPN DB,all earths connected correctly for installation
I recently did a small(ish) office which had amongst other things 3 radial cct's with high integrity earthing fed from a 10 way single phase board. I installed an extra earth bar to accommodate the extra cpc's but didn't use it in the end as I found a different way of doing it and still achieve compliance with the regs.
 
I think this is where the Regs trips it self up in situations like this, apart from a few additional terminals for main earths, bonding etc, no standard DB can fulfill the requirements for high integratity earthing comprising more than a couple of circuits and unless the additional earth conductors are cable I'd, it would make it very confusing for the next person coming along at a later date.
 
In one of our school sites there are some IT suites with more PC's than the OP's spec on each RFC. Not sure on exact numbers but I suspect there are as many as 15-20 PC's on some,which run without problems. One large suite had around 20-30 PC's running from a dedicated DB with a 30ma main switch....cant recall it ever tripping.
 
Last edited by a moderator:
Yea no probs connecting cpc's & numbering them, the hassle were connecting the corresponding earths of the rcbo's.Reckon another seperate earth bar would be the answer.
 
I think this is where the Regs trips it self up in situations like this, apart from a few additional terminals for main earths, bonding etc, no standard DB can fulfill the requirements for high integratity earthing comprising more than a couple of circuits and unless the additional earth conductors are cable I'd, it would make it very confusing for the next person coming along at a later date.
Exactly!
I always use cable markers (partek ones I find the best) but still think some clown who next comes along to add a circuit or two will bugger it up and just connect them together even though there's a label warning them of the setup.
 
Surely there wouldn't be a problem with say circuit 4 - lights sharing the no.4 earth terminal with circuit 2 - ring? If you're running out of terminal, just as long as the two from the ring aren't in the same terminal.
 
Its not really if the boards big enough you just end up with loads of spare ways that cant be used.

If you are saying that then, you must be installing a lot of high integrity circuits, then at the the planning stage you should have taken the need for extra earth bars into account.
Realistically how many circuits with the need for HI earthing would be required in, say a small to medium sized office installation, more to the point how may Electricians do you know who actually employ this method, I was involved in a recent EICR as an adviser where the RFCs where just chucked in, no notice taken of the possible earth leakage possibilities.
 
In one of our school sites there are some IT suites with more PC's than the OP's spec on each RFC. Not sure on exact numbers but I suspect there are as many as 15-20 PC's on some,which run without problems. One large suite had around 20-30 PC's running from a dedicated DB with a 30ma main switch....cant recall it ever tripping.

Ha, ha, ha, I'd have been back to test the rcd when they were next on holiday! :)
 
About 15 years ago we were guided 8 twin sockets not just due to earth leakage but due to the start up of those old monitors now we all use lcd which use a lot less power , i dont knowif the old monitors produced any earth leakage but i would of thought the lcd one don't produce any . And as said if as been designed for 15 sockets then thats down to the designer to worry about. Maybe pcs dont produce as much earth leakage as they did in the past .
 
As long as you wire the circuits, be they Rings or Radials correctly as per OSG 7.5 and adhere to the rules therin, as well as OSG 6.15 you should be OK
 
Can you refresh my memory to these points Pete, I Think the dog eat my copy ,few years back

Well 7.5 shows you how to wire the circuits and the reasons and 6.15 shows you what labels are required, nothing earth shattering (excuse the pun)
 
If the number of earth terminals supplied within the DB , is not sufficient to comply with the recommendation of the high integrity earthing .ask him how he would like them terminated?

If you have to ask him that question then he aint done his sums right.
 
Handy little PDF on the subject. http://electrical.------.org/wiring-matters/26/5437-earthing.cfm?type=pdf
 
What about the hip flask in the the sock?

Been married over 40 years Martin she knows all the hiding places it just aint worth it, should have put my foot down early on but anything for an easy, stress free life
 
A good idea would be to measure the actual earth leakage on the circuits with all sockets in use. I would be interested to know the results.

I used to do a lot of IT room installs for a previous company and the local authority spec was 6 double sockets per 32A ring circuit. This was based on one workstation (one pc and one monitor) per double outlet. I always thought this was a bit on the cautious side.

that seems cautious, i might rig up a temp socket with my pc later to check
 

Reply to Rcbo's in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
819
Hi there, I am looking for some advice re: putting new sockets and usb sockets in my home. Someone will be rewiring the entire house but I have...
Replies
19
Views
1K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock